Discuss Now surely in the real world in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

the pict

-
Mentor
Reaction score
247
Ze +R1&R2 should be more than Ze mmmmmmmmmm no Ze of .47 yes I know but its not TT its PME,d at the cut out but, Zs at socket .41 SSE have been so hopefully its resolved, anyone else had this
pict
 
Mhmm so to unravel that a bit, you @the pict find your Zs lower than Ze. It has been mooted (correctly in my understanding) that paralell paths on actual Zs may account for Zs being lower than Ze. The DNO came and tightened a PME connection at the cut-out. You say this was the reason you had lower Zs than Ze. I am a bit confused as I would have thought you would have a variable reading if the connection of earth to the PME terminal was poor? But is it really the answer, what did your subsequent test reveal, you left the issue open to conjecture with your statement.
 
Last edited by a moderator:
Mhmm so to unravel that a bit, you @the pict find your Zs lower than Ze. It has been mooted (correctly in my understanding) that paralell paths on actual Zs may account for Zs being lower than Ze. The DNO came and tightened a PME connection at the cut-out. You say this was the reason you had lower Zs than Ze. I am a bit confused as I would have thought you would have a variable reading if the connection of earth to the PME terminal was poor? But is it really the answer, what did your subsequent test reveal, you left me hanging a bit with your statement.
Sounds like you're waiting for the Orgasm Vorti
 

Reply to Now surely in the real world in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
Replies
12
Views
8K
Afternoon all. Bear with me on this one... Despite having been involved in the electrical industry for many years, I'm only just about to embark...
Replies
15
Views
2K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock