Discuss Odd fan wiring. in the UK Electrical Forum area at ElectriciansForums.net

GBDamo

-
Esteemed
Arms
Reaction score
3,010
Had three extractor fans, 15yr old, all non functional which was odd to start with.

All three were supplied with a three core and earth from a fan isolator, all very normal but the fans were not timer fans, odd.

Was on the verge of going out to get new ones but checked the voltages at the fans and got 240V PL-N and 70V SL-N?

Had a look in the fan isolators and all three had the over run timer wired up in the fan isolator back box.

Has anyone come across this before?

Could someone with the technical genius explain why this might be done, bearing in mind there was a three core and earth pressent.

[/URL]

These were the timers being used.

What are the potential issues with these being remote from the fan as opposed to in the fan?
 
You'd still need a second live at the fan for run on, via the controller, so I would imagine there would be provision. Two signals, one for run, one for run on.
 
You'd still need a second live at the fan for run on, via the controller, so I would imagine there would be provision. Two signals, one for run, one for run on.
No, the fans only had a L and N terminal, with the over run function carried out by the unit at the fan isolator which commected to Sl, PL and N and out puttedd to the fan via a sinle live wire.
 
No, the fans only had a L and N terminal, with the over run function carried out by the unit at the fan isolator which commected to Sl, PL and N and out puttedd to the fan via a sinle live wire.
That's understandable. One line being controlled in either. But you said they were wired in 3 core. If so, how were they connected?
 
That's understandable. One line being controlled in either. But you said they were wired in 3 core. If so, how were they connected?
Which is odd, they were and the PL was live and taped over.

I don't see the need to do this here although it could be an option where a 3core is not available and a time fan is required.
 

Reply to Odd fan wiring. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
659
Good afternoon everyone. I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on...
Replies
92
Views
8K
Hi all, I'm in the UK and have recently had a ducted extractor fan Mixflo 200W with timer fitted. The fan comes on with the pull cord and runs for...
Replies
6
Views
238
Hi guys, I'm an apprentice electrician and have been doing some basic work on my bathroom with what I've picked up on site. I've split the mains...
Replies
5
Views
1K
Hi there, I'm trying to wire an extractor fan (Manrose 4" / 100mmm with timer) I don't have too much knowledge about Electricity but I'm very keen...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock