Morning guys,

Just been to look at a CU change and there was a bit of an oddity with the PME connection in the old black cut out.

Looking at the history, it used to have a earth rod but at some point the DNO upgraded the network but didnt provide an earth connection, but someone has connected there own.

There has been all sorts of stuff added and taken away over the years, but it appears that the PME connection comes out of the top of the cut out opposite the neutral connection, rather than the little PME terminal on the side.

In my wisdom i neglected to take a picture, but i did a quick test and the results were good with 0.30ohms and 0.77ka.

Can i leave it like this or should i inform the DNO?

My only concern is that they are not aware and have it recorded as such.
 
DIY pme connection is not allowed and possibly unsafe.
Get the dno out, I think you might be able to see some bare copper at the service head? Wink
 
It's not uncommon to find the earth cable put out from the additional neutral knockout, not the designed one on the side. If the rest of it looks intact and solid then I'd suggest just making a note of it on the report - you can't code it as it's not the consumer's kit therefore outside of your remit/expertise (theoretically....). If you smell a rat then have the customer report it to their energy supplier to send a meter inspector out rather than the DNO, that way you can't get a surprise bill for a DNO callout....
 

Reply to Odd PME connection on CU change survey. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys, Had an issue at a recent survey where doing a quick check and found we had pme with a reading of 0.44 ohms. Called the network and they...
Replies
5
Views
363
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
532
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
678
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
748
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
844

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock