Hello All,

I have won a contract for installing motion sensors in to an office building.

I have to carry out all the works during office hours and I am unable to isolate the supply of the necessary circuits at the consumer unit (there are individual isolators to isolate sections of circuits at points through the offices). Due to this, I will be issuing MWC's for all work carried out but will only be testing the section of the circuit I have /will install.

Realistically, I can only carry out R1+R2 tests and will note the reasons why on the cert.

Will this be sufficient to cover my back should there be issues with other sections of the circuit when this installation has a periodic carried out, which is due in 6 months time?

Any advice is always helpful.

Thanks.
 
your problem is that your R!+R2 readings should be for the whole circuit from the DB to the end of line. just taking readings from the individual isolators is no good. you will however be able to take Zs readings without isolating at the DB. you could possibly put the R1+R2 down as a limitation. also, are these isolators able to be locked off? some pratt might switch them on while you are working.
 

Reply to Office lighting PIR's in the Australia area at ElectriciansForums.net

Similar Threads

I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
555
Hi. I'm an I.T.. engineer with some outdated electrical experience. I qualified C&G 2330 17th edition about 15 years ago, but my only experience...
Replies
4
Views
799
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
795
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
661
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock