Discuss Old black red wiring in bathroom in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

P

Paul Heritage

Im a tenant living in a house in Liverpool, I have only recently moved in but noticed straight away the lack of any earth wires in the metal light fittings. I flagged this up and the landlord came round and replaced all the fittings to plastic while I was away on business. On returning I have checked the bathroom light which flickered to find it was also metal, no earth and 240v 60 watt bulb. I haven't done electrics for a while but thought there were different regs for wet rooms but don't know anything about old wiring. I have also found out that the landlord has added a socket in the kitchen which I thought needed to be done by an electrician. Am I needing to get an inspection done even if the landlord says it doesn't need one?

Any help would bee appreciated, thanks.
 
your landlord should have had an inspection done on change of tenancy.
 
Makes a change for a landlord to do at least something, we all know what they should do but round here they are all blood sucking loaches and wont spend a penny unless you go legal.


If your that concerned get a local sparks to do a quick visual inspection to confirm your findings, that way you have at least some qualified pressure to push to get a full inspection done.
 
Im a tenant living in a house in Liverpool, I have only recently moved in but noticed straight away the lack of any earth wires in the metal light fittings. I flagged this up and the landlord came round and replaced all the fittings to plastic while I was away on business. On returning I have checked the bathroom light which flickered to find it was also metal, no earth and 240v 60 watt bulb. I haven't done electrics for a while but thought there were different regs for wet rooms but don't know anything about old wiring. I have also found out that the landlord has added a socket in the kitchen which I thought needed to be done by an electrician. Am I needing to get an inspection done even if the landlord says it doesn't need one?

Any help would bee appreciated, thanks.

Before jumping in and giving you landlord some stick, check your tenancy agreement. I have seen agreements where the tenant has the responsibility for getting stuff like this done. Not right in my opinion but, you could end up with a big bill if you are not careful. If it is his responsibility, and he has used a letting agent, then get onto them about it, as they may be able to force his hand as they have put you into a potentially dangerous predicament.

Cheers...........Howard
 

Reply to Old black red wiring in bathroom in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
717
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
801
our dimmer switch stopped working after 7 years so went to replace it at the weekend. When I opened it up, the black wire was in the common slot...
Replies
0
Views
260
Hi, I am installing a new bathroom fan. We had an electrician who ran 14/3 into a junction box. The black feeds a led light and the red was...
Replies
1
Views
728
For the bathroom, want them matching and one needs to go over the shower. Also need to be ok with insulation over the top. Ideally fit in the...
Replies
2
Views
265

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock