Discuss Old Firebird 90 thermostat issue? in the DIY Electrical Advice area at ElectriciansForums.net

Hi sorry not had the chance to check the timer until tonight below I've attached the readings, all other terminals are not live with the mains on.

The L and number 2 have the mains power.

Both valves are on auto not on manual
 

Attachments

  • sketch-1710266213640.png
    2.3 MB · Views: 10
  • DSC_6421.JPG
    128.9 KB · Views: 5
Hi sorry not had the chance to check the timer until tonight below I've attached the readings, all other terminals are not live with the mains on.

The L and number 2 have the mains power.

Both valves are on auto not on manual
Thanks for the update.
I don't understand why you have a voltage on terminal 2, which is the signal for "HW off", which I thought was only ever used for Y-plan systems.
Can you remind me - is the motorised valve you have a 2-port (pipe in and out) or a 3-port (3 pipe connections, one coming up opposite the motor)?

Update: having refreshed my memory of what's inside a 3-port valve, if you do have one, then I would expect there to be a voltage on terminal 2 as indicated by your meter (being fed via diode and resistor in the motorised head), assuming the valve was in the CH position.

If you do have a 3-port valve/ Y-plan system, and assuming wiring is traditional y-plan, then I think the wire currently in terminal 2 (which you measured live) should actually be in terminal 1. I'm assumoing that brown wire goes to the cylinder stat.
I believe normally the "CH OFF" terminal is not used, and the "HW OFF" terminal is used.
You might try transferring that wire, but I'm not convinced it will necessarily fix the problem!
 
Last edited:
Thanks for the update.
I don't understand why you have a voltage on terminal 2, which is the signal for "HW off", which I thought was only ever used for Y-plan systems.
Can you remind me - is the motorised valve you have a 2-port (pipe in and out) or a 3-port (3 pipe connections, one coming up opposite the motor)?

Update: having refreshed my memory of what's inside a 3-port valve, if you do have one, then I would expect there to be a voltage on terminal 2 as indicated by your meter (being fed via diode and resistor in the motorised head), assuming the valve was in the CH position.

If you do have a 3-port valve/ Y-plan system, and assuming wiring is traditional y-plan, then I think the wire currently in terminal 2 (which you measured live) should actually be in terminal 1. I'm assumoing that brown wire goes to the cylinder stat.
I believe normally the "CH OFF" terminal is not used, and the "HW OFF" terminal is used.
You might try transferring that wire, but I'm not convinced it will necessarily fix the problem!
It only has two electric valves, another thing I noticed also is that when the mains is on and it fires up (power to the timer but not switched to on to open the valves) the valves are powering up and opening anyway.

I just don't understand how it's just decided to do the continuous running off the mains. As it didn't happen with any one of the alterations or new items within the setup.
 

Attachments

  • DSC_6440.JPG
    528.1 KB · Views: 4
  • DSC_6441.JPG
    395.2 KB · Views: 4
It only has two electric valves, another thing I noticed also is that when the mains is on and it fires up (power to the timer but not switched to on to open the valves) the valves are powering up and opening anyway.

I just don't understand how it's just decided to do the continuous running off the mains. As it didn't happen with any one of the alterations or new items within the setup.
Thank you for the clarification.
Now I understand it is an "S-plan" system, that makes things clear.

I thought it might be a motorised valve problem, but now you say that the minute you turn the setup on, both valves motor on whatever the programmer setting, so now I'm thinking the programmer is not doing the right thing!
You will see from the diagram that the valves are supposed to supply the power to the boiler, but only when they are activated. What is turning them on other than the programmer?
(Note the diagram shows a boiler that has both L and SL terminals, but I believe yours has just a L feed. So there should be no direct connection from your switched spur to the boiler as in the diagram below. The only source of power to the boiler should come from the orange wires of the motorised valves,)

The wire on terminal 2 of your programmer shouldn't be there in a typical 2 valve system, so I would suggest disconnecting it, isolating the end, and trying the setup again.

If you replaced the motorised valves, are you sure the motor supply wires (blue and brown) go to the correct places.
ie you have wired the valve brown wires to their respective thermostats, not directly to live mains?
Or to put it another way, were grey and brown wires inadvertently swapped?

IMG_0501.jpeg
 
Last edited:
Thank you for the clarification.
Now I understand it is an "S-plan" system, that makes things clear.

I thought it might be a motorised valve problem, but now you say that the minute you turn the setup on, both valves motor on whatever the programmer setting, so now I'm thinking the programmer is not doing the right thing!
You will see from the diagram that the valves are supposed tonsupply the power to the boiler, but only when they are activated. What is turning them on other than the programmer?

The wire on terminal 2 of the programmer shouldn't be there in a typical 2 valve system, so I would suggest disconnecting it, isolating the end, and trying the setup again.

View attachment 113907

Thank you for the clarification.
Now I understand it is an "S-plan" system, that makes things clear.

I thought it might be a motorised valve problem, but now you say that the minute you turn the setup on, both valves motor on whatever the programmer setting, so now I'm thinking the programmer is not doing the right thing!
You will see from the diagram that the valves are supposed tonsupply the power to the boiler, but only when they are activated. What is turning them on other than the programmer?

The wire on terminal 2 of the programmer shouldn't be there in a typical 2 valve system, so I would suggest disconnecting it, isolating the end, and trying the setup again.

View attachment 113907

Thank you for the clarification.
Now I understand it is an "S-plan" system, that makes things clear.

I thought it might be a motorised valve problem, but now you say that the minute you turn the setup on, both valves motor on whatever the programmer setting, so now I'm thinking the programmer is not doing the right thing!
You will see from the diagram that the valves are supposed to supply the power to the boiler, but only when they are activated. What is turning them on other than the programmer?

The wire on terminal 2 of your programmer shouldn't be there in a typical 2 valve system, so I would suggest disconnecting it, isolating the end, and trying the setup again.

If you replaced the motorised valves, are you sure the motor supply wires (blue and brown) go to the correct places.
ie you have wired the valve brown wires to their respective thermostats, not directly to live mains?

View attachment 113907
I understand the diagram and what your saying, there was no re wiring required for the new valve just plugged it in.

So both valves come on as soon as the mains is switched on, they can't be controlled via the controller at all, only way is to pull off the timer and then it cuts out (or switch of mains)

There is two lines coming into the (L) is that right? Is that for both the valves?

As testing before I unplugged each valve seperately and it was the same (powered up via mains with no control from the timer) so wouldn't that rule out the valves?

If it's not raining tomorrow I'll get out and have a decent look hopefully
 

Attachments

  • Screenshot_20240316-174715.png
    900.5 KB · Views: 8
I understand the diagram and what your saying, there was no re wiring required for the new valve just plugged it in.
OK, so as if you replaced valves like for like, and just plugged in the existing cables as it were?
So both valves come on as soon as the mains is switched on, they can't be controlled via the controller at all, only way is to pull off the timer and then it cuts out (or switch of mains)
So the valves must be getting power from the 'timed' side of the timer, else the boiler would carry on when you pulled it out!
There is two lines coming into the (L) is that right? Is that for both the valves?
I don't know why there are two wires. The second could be the live feed for the microswitches in the valves.
(But the 'extra' wire is single core cable, not a flex, so is part of the house wiring. Do you know if the wiring from here to the boiler is done in twin and earth, or in a conduit? Doesn't seem to be flex which is often used if the boiler is nearby)
As testing before I unplugged each valve seperately and it was the same (powered up via mains with no control from the timer) so wouldn't that rule out the valves?
Yes I agree that rather suggests it cannot be a fault in one valve, it's something else
If it's not raining tomorrow I'll get out and have a decent look hopefully
Traditionally there would be a 'wiring centre' where wires from supply, timer, valves, boiler all congregate, and that's where the fault finding is usually undertaken. It looks to me as if that Hensel junction box on the right might be your wiring centre - is that where the cable from the timer and internal cables for the motorised valves go?
Is it possible something has got disturbed in there (eg by a cable being inadvertently pulled externally and affecting something inside)?

Otherwise suspicion falls on the timer, as that seems to be supplying power when it's plugged in (whatever it's set to!) but if wired as most are, turning the HW thermostat down, and simultaneously the CH thermostat down, should stop the boiler, even if the timer is faulty!
I can't remember, did you try that?
 
Last edited:
Hi mate

Managed to get out today and have a look around.

The main junction box looks to be on all wires are tight and connected.

I also removed the (2) wire from the controller pin and it's still exactly the same with no response still comes on as soon as mains switch is on.

The thermostat inside the burner unit when turned down does cause the burner to turn off so that is working on that side too.

The last picture there is the inside thermostat should that also make it cut out if turned right down? Could this be at fault or is it still looking like the controller?

Cheers
 

Attachments

  • DSC_6490.JPG
    56.1 KB · Views: 12
  • DSC_6488.JPG
    387.7 KB · Views: 10
  • DSC_6486.JPG
    319.6 KB · Views: 6
  • DSC_6486.JPG
    319.6 KB · Views: 6
Thanks for persevering!
The wiring in that box is unconventional, in that the oranges are connected together presumably to send power to the boiler, and the greys hopefully go to DHW and CH thermostats. The colours are normally the other way round, but it doesn't matter - same result so don't change it.

There's visible bare copper showing at the ends of the cables in some choc-blocks, which is poor.

Normally power goes in series from (eg) the fused spur to timer, then to thermostats, then to motorised valves, and then when the motorised valve operates it's end microswitch, power is fed to the boiler.
Any one part in that chain can stop the boiler working, but not make it stay on (that needs all the other parts of the chain to be on too).
So actually I can't see how the wall thermostat can keep the boiler running if the timer is not providing it with power, so the obvious thing is the timer is "stuck" on.
Also when you unplug the timer the boiler stops, so that supports the theory!

I'll give this some more thought🤔 and get back sometime.
 
Hi fella

So I replaced the timer with a

Honeywell thr860swe tm2

Now it's all good bar a few bugs.....

I think the wiring for the timer is the problem now.



I haven't altered it just swapped it over as it was and now the 1&2 motorised valves are powering up and turning.

But I do have a strange problem with controlling individually.


Power - ON (all good now not continuous running)


Switch ON for Heating/Rad, valve turns

Burner fires up and does the right thing


Switch ON Hot water, valve turns and comes on

The problem now is when I turn off the HW and the valve stays open

so am I right in thinking I have the OFF wiring for the HW is incorrect?

pic 1 - old timer wiring

pic 2- old timer wiring diagram

pic 3 - new timer diagram


Thanks for all the pointers I'm getting a bit better at this now but I'm used to cars with colored wires so much easier than just a bunch of brown wires 😑
 

Attachments

  • Screenshot_20240420-101636.png
    965.5 KB · Views: 4
  • Screenshot_20240420-101554.png
    1.1 MB · Views: 4
  • Screenshot_20240420-101557.png
    813.1 KB · Views: 3
Sorry wrong diagram attached there (that's the 1 channel version)

This is the correct new Diagram (R) and old (L)
 

Attachments

  • 1713637167446.png
    2.2 MB · Views: 2
i was just about to post saying that was single channel programmer!!
I can't tell how you've wired it from the pic though!
They do seem to have equivalent terminal numbers, so if you just transferred the wires over it should be equivalent.
 
Try disconnecting the "central heating off" wire from terminal 2 and insulate it (eg Wago connector or choc block or similar) and tuck it out of the way. Just temporarily.
See if it makes any difference.

There's something weird about the wiring of your setup.
The "off" connections on a programmer are normally only used for Y plan systems.
Yours is an S plan, so I wouldn't expect either "CH off" or "HW off" terminals to be used.
In my experience the "CH off" terminal is never used in either of the above traditional schemes, so I don't know why you have a wire on it in the first place (or have any idea where it might go!)
 
Last edited:

Reply to Old Firebird 90 thermostat issue? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

My mother in law has a new bungalow (3 years old) with an electric only system. It's controlled using an SM1 controller which I've set to come on...
Replies
0
Views
624
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
932
m having a bit of an issue that is proving difficult to resolve. For 2 years I have been having no problems with my setup. I have a 3 zone house...
Replies
1
Views
1K
Good afternoon chaps, I have an Alpha E-Tec 33 combi boiler (with Google Nest 3rd Gen thermostat) that occasionally fails to put out hot water...
Replies
10
Views
951
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
614

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock