Search the forum,

Discuss Old problem with circuit length calcs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

sivoodoo

Sorry to bring up an old post but im confused.

I have carried out tests on a kitchen ring final wired in 2.5mm/1.5mm T&E, results as follows:

r1=0.36 rn=0.34 r2=0.59

I then joined leg 1 of line conductor to leg 2 of cpc and leg 2 of line conductor to leg 1 of cpc and measured the R1+R2 at each socket outlet, the highest reading for R1+R2 = 0.26.

We know that:
1.5mm = 12.10 mOhms/m
2.5mm = 7.41 mOhms/m

12.10 + 7.41 = 19.51

19.51 mOhms/1000 = 0.01951Ohms/metre

therfore R1+R2 / 0.01951 = length in meters

0.26 / 0.01951 = 13.326m

But the cable I have used is about 35 meters?

Could someone please explain my results and offer any advice

Thank you all
 
the readings seem ok to me, don't forget r1r2 will be double the length taking you up to 26m,I doubt if your meter is 100% accurate, I wouldn't worry about it if I was you;)
 
The numbers look fine considering your readings.

If I was reviewing those figures I would be very satisfied.

(r1 x 1.67) should equal r2 - (0.36x1.67=0.60) You measured 0.59 which is spot on.

(r1+r2)/4 should equal R1+R2 - ((0.36+0.59)/4=0.24) You measured 0.26 which is expected.



As for the length, those numbers will never be 100%, for a kitchen ring final these numbers make perfect sense.
 
Last edited:
Sorry to bring up an old post but im confused.

I have carried out tests on a kitchen ring final wired in 2.5mm/1.5mm T&E, results as follows:

r1=0.36 rn=0.34 r2=0.59

I then joined leg 1 of line conductor to leg 2 of cpc and leg 2 of line conductor to leg 1 of cpc and measured the R1+R2 at each socket outlet, the highest reading for R1+R2 = 0.26.

We know that:
1.5mm = 12.10 mOhms/m
2.5mm = 7.41 mOhms/m

12.10 + 7.41 = 19.51

19.51 mOhms/1000 = 0.01951Ohms/metre

therfore R1+R2 / 0.01951 = length in meters

0.26 / 0.01951 = 13.326m

But the cable I have used is about 35 meters?

Could someone please explain my results and offer any advice

Thank you all


To calculate the length of your cable you need to add your R1 and R2 readings.
ie 0.36 + 0.59 = 0.95

0.95 / 0.01951 = 48.7M

or add your R1 and Rn readings
ie 0.36 + 0.34 = 0.70

0.70 / 0.01482 = 47.25M

Using these figures i would calculate your cable run to be between 47 & 49 M
 

Reply to Old problem with circuit length calcs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
856
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Hi guys, I just need help with something really basic that I’m struggling with in terms of calculating resistance (as opposed to measuring)...
Replies
11
Views
12K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top