Search the forum,

Discuss once again maximun demand sorry! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

W

wirvine88

Hi all,
sorry to bring this up again but I cant quite find the answer I need for an assessment

As part of a rewire the ground floor has 20 double 13amp sockets but 9 of these are in the kitchen.

I have been told the kitchen is drawing sockets will have:
13.3 amps from a washer dryer
13.3 amps from a dish washer
1.7 amps from a fridge

How do you work out the maximum demand as I keep getting really high figures!

is it worth going for the kitchen on its own ring of 32 then the other 11 sockets on a 32amp mcb
or does it all go on a 32amp mcb- looking at diversity as i understand it for sockets-13amp for one then 50% for the rest but thqt for just the 13 sockets is = 136amps?

I have spent so much time on this I have completly confused myself so any help would be great!

Cheers
Will
 
you need to consider diversity. i.e. not every load will be on at the same time. your 2 appliances you mention will each be about 2kw (with heaters on), that's 9A each. to estimate the demand, take it as 9A for 1 appliance then 0.4 x the total of the other loads on the circuit.
 
Jocks apart, Lets say you clamped the RFC and watched over time the values being displayed.

You would probably find that with everything running you might have a constant 12A and the occasional jump to 20, 25, 30A and then back to a steady 12 - 15A. The regs make an allowance for these types of short overloads so no problems there. .

But how do you justify this by prediction? Good point I here myself say.

This can be achieved by various methods and takes years of experience to know how combinations of different types of load function together.

Probably better in your case to split the circuits so that the 9 circuits in the kitchen are on a separate 32A ring and the rest can either be placed on their own 32A RFC or fused down to a 20A radial.
 
the 9 circuits in the kitchen.

bloody big kitchen to have 9 circuits. LOL.
 
'Probably better in your case to split the circuits so that the 9 circuits in the kitchen are on a separate 32A ring and the rest can either be placed on their own 32A RFC or fused down to a 20A radial.'

Strong beer in the forum pub tonight (9 circuits)!

 
'Probably better in your case to split the circuits so that the 9 circuits in the kitchen are on a separate 32A ring and the rest can either be placed on their own 32A RFC or fused down to a 20A radial.'

Strong beer in the forum pub tonight (9 circuits)!


Those bloody socirkets its something to do with the jockets scotets Now I know why they use straps to hold in the jocks.....
 
Oh ar, there are some biguns round here.....


Electrical trainee exams should now include a question under the diversity label,can they fill ackbarthestars kitchen
icon12.png
 
Hi all,
sorry to bring this up again but I cant quite find the answer I need for an assessment

As part of a rewire the ground floor has 20 double 13amp sockets but 9 of these are in the kitchen.

I have been told the kitchen is drawing sockets will have:
13.3 amps from a washer dryer
13.3 amps from a dish washer
1.7 amps from a fridge

How do you work out the maximum demand as I keep getting really high figures!

is it worth going for the kitchen on its own ring of 32 then the other 11 sockets on a 32amp mcb
or does it all go on a 32amp mcb- looking at diversity as i understand it for sockets-13amp for one then 50% for the rest but thqt for just the 13 sockets is = 136amps?

I have spent so much time on this I have completly confused myself so any help would be great!

Cheers
Will

Regardless of anything else, surely commonsense should tell you that a kitchen should be allocated it's own socket circuit. It's the one room in the house/flat where most, if not all the higher rated home appliances are going to be located....
 
My personal preference is a RFC upstairs, a RFC downstairs and a separate RFC or radial for the kitchen.

I also like to put the kitchen on an RCBO so all the frozen food isn't lost if there's a problem elsewhere in the house.
 
My personal preference is a RFC upstairs, a RFC downstairs and a separate RFC or radial for the kitchen.

I also like to put the kitchen on an RCBO so all the frozen food isn't lost if there's a problem elsewhere in the house.


Which was exactly my point!! You need a minimum of 3 socket circuits in an average sized house. The day's of having a single RFC to cover the whole houses power needs, have long since passed. lol!!
 
we get by quite happily with 2 20A radials. sod all these energy guzzling appliances.
 
I went 'Froggie' on one job once.

Two bedrooms over three floors plus a Kitchen.

One rfc for the kitchen and one 16A radial per floor. I might have got even more excited and used separate radials throughout the kitchen, but I ran out of DB space.

Radials are now the way to go. ............
 
Thanks very much for all your help guys,
I love reading these threads when pople get carried away "its surely commen scense..." I am sure it is when your qualified but when your learning theres alot to work out!

Cheers everyone
 
Have electrical installation standards lowered to accommodate the lack of skill and knowledge of the installers?
Why in gods name would anyone install a radial unless it is to feed a specific piece of equipment?

Diversity is purely a matter of common sense. I ran my flat as an experiment using a 16A MCB for a week. It never tripped.
 

Reply to once again maximun demand sorry! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K
Bit of advise if anyone has time.. I have a customer who brought a new kitchen from wrens. Customer has had the route to the kitsch redecorated...
Replies
3
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
809
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock