Search for tools and product advice,

Discuss One way 240v flow HOW in the UK Electrical Forum area at ElectriciansForums.net

Vaf888

DIY
Reaction score
1
Good Morning.

I have a fused spur which has 2x240v inputs and 1x240v out put.

The 240v inputs are from heating control panels. One is from a timer clock for hot water and the other from a large 1000l hoh water storage tank. The ouput is to the oil burner.

So the question is when i have i have a single input switched on with other input off the off input is getting a live feed, from the on input. Is there anything that can be wired in to make the flow one way only.

Thanks
 
The way to stop backfeeding , which is what you appear to describe, is to use a relay on each input.

What is the effect of the backfeed, both appear to be connected with Hot water, the issue is normally between Hot water and Heating?
 
Hi.

Thank you for the prompt response.

The backfeed means that the hotwater pump is constantly on. I have that circuit on the clocks, so effectively its ignored as the temp control of the storage tank is backfeeding it when it is maintaining the heat.

What type of relay is best to put on the inputs.

Thanks
 
I have a fused spur which has 2x240v inputs and 1x240v out put

Is this a commercially made device, or are you saying there are two separate feeds connected to the input of one ordinary fused spur unit? (Which is obviously not a standard thing to do, and if the two sources are separate circuits it is highly dangerous as the isolation and OCPD is rendered inoperative)

The solution as mentioned above is to use two relays. Each relay's coil is controlled by one of the existing supplies. The spur box gets a new permanent feed, then its output goes through the two relay N/O contacts in parallel to the burner.

The relays need to have 230V coils and contacts rated for the load current of the burner.
Here's a completely random example:
16A 230V DPST DIN rail relay
 
The problem I have found with conventional relays is the noise they make when operating, I tend to use electronic relays instead, sorry don't have a random example.
 
Hi.

Attached is a basic diagram of the setup. In order to stop the back feed I have an isolation switch on the feed so that when I only want hot water I can turn off the hot storage control and just use the isolator. Its not ideal.

If I were
1584717072902420813428320832177.jpg
to install the two relays, would they simply be wired into the circuits as per the second pic

Thanks
 
Last edited by a moderator:
Just checker the system. If the hot tank is not calling and the water circuit kicks in its not drawning any hot water as the pump on the boiler is not activating as the hot water circuit has no power due to the isolator. So need the relays.

I recently changed to oil from a wood pellet boiler which had two control inputs with zeroo volts. So this is the nightmare. Errrr
[automerge]1584736801[/automerge]
What if i went back to a zero volt trigger? Is there a easier solution there.?
 
Is there any particular reason why this system couldn't be plumbed and wired using 2 port zone valves? These effectively act as relays, but the coil in the relay is replaced by the syncron motor in the valve. This has the added benefit that the boiler and pump won't receive a fire signal until it is physically proven that the hydraulic circuit is open, so prevents boiler lockout on overtemp.
 
Its has a two port value system on the hot water side. I have wired it to the call feed, but the back feed from the hot storage controller is causing the issue. Should i try to wire it back to the value in some way, or would i have the same back feed issue

Thanks
 
If you were to add a 2 port valve to the heating side as well, and wire as typical S Plan, you'd achieve the separation you require. That would be my approach unless there is a specific reason why that can't be done.
 
Hi

The hesting side i.e does have a 2 port value. Only the repol tlr2 control to regulate the temp in the storage tank. The tlr2 controller has a bridged 240v feed within the call for heat when required. As far as i can tell there is no back feed issue here, if the hot water circuit is on.

Should i try an trace the hot water side back to the two value, or would the back feed activate it too.

Thanks
 
Just looked again at your diagram. Seems you have timer in Parallel with Stat.

Generally you'd wire in series. So Timer passes 'on' signal to stat, if water is cool, stat will pass on signal to valve. Valve then opens, activates microswitch, and sends fire signal to boiler.

Not sure if I fully understand the setup though. Got any model numbers and a system schematic?
 
Hi There

Thank you for your help.

I have attached the boiler manual and from i read there is no pump overrun or dual inputs for the CF or HW. Just a mains 240v connection. All other switching is controlled externally. If this makes sense.

Apologies the rough sketch i provided is to basic.

On the hot storage CH side i have repol tlr2 controller.

On the hot water clock HW side i have the horstmann xl27 which activates a value system and motor. These are not in the sketch, so apologies, but they are series linked. As if the value is open the pump for the HW kicks in only if the cylinder stats require them. So all is good there.

Just trying to solve the back feed. Cant figure out why i need to do it this way as a dual input on the boiler would have been so much easier.

Is there a external dual input available on the market at all.

Thanks again
 

Attachments

  • grant-vortex-boilerhouse-installer-uk-doc-0128-rev-10-january-2020 (1).pdf
    7.3 MB · Views: 0
Hi,

A schematic of the hydraulic side of the system would be handy. If I'm reading this properly, you have 2 tanks? At large thermal store controlled by the Resol Controller, which is used for Central Heating? And a Smaller DHW cylinder for the Hot Water?
 
Yes. Thats it. Only the two zones on the xl27 clock are connected to two hot water cylinders, and when the cirucuit is on a pump on the hot water line activates to draw the hot from the main feed connected to storage tank.

I am not the original owner of the house, but came across these drawings for the hot water.

Thanks
[automerge]1585057315[/automerge]
Two values for the two tanks with the hot water pump connected below.
 

Attachments

  • Screenshot_20200324_130408_com.whatsapp.jpg
    45 KB · Views: 9
  • Screenshot_20200324_130420_com.whatsapp.jpg
    53.3 KB · Views: 10
  • IMG_20200324_133859.jpg
    93.2 KB · Views: 10
  • IMG_20200324_133842.jpg
    80.1 KB · Views: 10
Last edited:
Hi,

Thanks for info. Only had a quick skim read, but it looks like the boiler fire signal should only be supplied from the Resol controller. That will control the temperature in the buffer tank and tell the boiler when it needs heat.
The zone valves for the hot water cylinders simply need to open, and when open activate the pump to circulate from the buffer tank, no connection to the boiler should be needed. As the heat is drawn out of the buffer tank, the resol controller will detect the temp drop, call for heat, and fire the boiler.
I think that is how it should be set up?
 
Yeap i agree and that works, but does that mean the boiler pump always needs to be on. I have noticed that if the repol is calling for heat, the boiler fires along with its pump, and if the hot water is on its all good. But if the repol is off the boiler along with its pump is off. Hot water kicks in and the hot water pump starts. Because the boiler pump is off there doesnt seem to be a flow.

Obvious then when the CH is off during the summer i would turn the Repol off and close of the inlet and outlet to the storage tank and then switch to a direct feed via the insolation switch.

Question do pumps internals lock with no power and would a temp set of 50 degrees to the hot store be enough to heat the water. If i jump to the summer scenerio the temp from the boiler would be 70 plus.

Thanks
 
Hi Mike. Yes both pumps work.

Thanks
[automerge]1585067699[/automerge]
Ideally for the HW both pumps, and for the CH just thr boiler pump. If i can sort the bavk feed problem it would me that can have the direct HW direct to the boiler via the junctioned spur. So when the HW clock kicks both pumps are on. If the HW is off and the CH is on, the live feed from the CH is turning the HW on via the back feed. Thats why have the manual switch in there at the moment.

Cheers
 
Last edited:
Not sure. How can i tell
[automerge]1585080162[/automerge]
There is a large red cylinder connected on the main return of the boiler of that hrlp
[automerge]1585080934[/automerge]
There is a large red cylinder connected on the main return of the boiler of that hrlp
 
Last edited:
Hi Mike. All the motorised values are working.

I need a solution to thw back feed. Looking at 25amp no nc contractor with a coil. Would this work to stop the back feed?

Thanks
[automerge]1585088112[/automerge]
I dont so many connections as the HW on has two wires.

Look electrical supplier suggested this, but not sure.
 

Attachments

  • IMG_20200323_090039.jpg
    71.2 KB · Views: 2
Need to be careful here. If cylinders are unvented, and you are trying to alter the controls, then this can have disasterous consequences.
I would recommend you get a professional to look at the system first hand. For what it's worth, I don't see the issue with leaving the resol controller on in the summer, these buffer tanks are normally very well insulated, and without altering pipework, chances are you're trying to draw boiler flow water through the buffer direct to cylinders without mixing, which is unlikely to work. With some pipework mods, a safe and operable system could be made to bypass buffer for a winter and summer mode, but I wouldn't suggest it's a DIY job.
 
The only thing i have changed on this is the heat source. Which was a wood pellet burnsr. It was wired with two. Zero volts inputs CH and HW. Now that i have changed the heat source to oil, the new burner only has a single 240v input.

I did not think the change of the heat source would have any impact on the actual plumbing side of things, just the electrical side due to the single input. Am i being stupid here.

Do you know about the contractor?

Thanks
 
Thanks for all your help guys. After a bit of research, it turned out the original contactor which was in the system was wired incorrectly by the installer so not activating the coil.
 

Reply to One way 240v flow HOW in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Is there such a thing as a double breaker that has a separate DC and AC line passing through it? I need a 12v (25 amp) line and a 240v (15 amp)...
Replies
1
Views
705
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
I have pulled out an old evaporative system I purchased many years ago from storage to have a look at it and see if I can get it running. Was...
Replies
1
Views
234
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock