Having issue with open neutral. Site won't let me post any details saying its spam...not sure why?
Discuss Open Neutral Issue in the USA Electrical Forum area at ElectriciansForums.net
Are you trying to attach something to your post? Your free keyed posts are displaying OK.It won't let me respond with any details David. Thanks for trying to help. Any advice on how to post on here?
Generally, opening attachments, especially PDF's, from unknown sources (and members) can be bad. Adobe don't have the best security measures. That's why we don't see Flash files on websites anymore.I was going to open what col89 sent but i did not want to open in case it was a spam.
What makes you think you have an open neutralIt won't let me respond with any details David. Thanks for trying to help. Any advice on how to post on here?
Are you an electrician ColoradoTest, 5th message
[automerge]1567366145[/automerge]
Hi, I'm hoping to get a bit of advice on an open neutral problem I'm having in my house. Below is a short summary of the issue:
What could the issue be? Is it possible the neutral wire is bad? That seems unlikely. What is odd, is all I was doing was replacing the outlets in the master bedroom, but somehow the open neutral has come up in the room next to the master even though I had done nothing in that room at all. Any advice is greatly appreciated. Thank you!
- Was painting my master bedroom and updating the outlets from the dreary almond color to newer white ones.
- House was built in 1986. Wiring is okay, but not done super well. Many outlets have multiple hots & neutrals inserted in the back clips of the old outlets instead of pig tailed together and screwed in.
- After replacing the last outlet in the bedroom and going to test them, I found I was not getting power to any of the outlets in the room. Used an outlet tester and found I was having an open neutral problem.
- Worked on attempting to trace the problem and what was going on. After a few days of working on it off and on, I started trying to trace the full circuit. Initially I thought the circuit only covered the master bedroom, but found that 2 outlets and 1 switch in the bedroom next to the master was on the same circuit.
- Found the outlet closest to the circuit breaker on the circuit, and used the outlet tester and it is working fine. Next in line downstream is a light switch that is connected to the second outlet in the other bedroom. At that point is where the open neutral is showing.
- I have replaced the first outlet on the circuit with a newer one, I have the 3 hots screwed in, took the 3 neutrals and pig tailed them together and have it screwed in, and is grounded. Still getting an open neutral on the switch and 2nd outlet in the other room.
Do you think you got the polarity crossed when you changed other outlets?Are you an electrician Colorado
Are you an electrician Colorado
[automerge]1567367876[/automerge]
Do you think you got the polarity crossed when you changed other outlets?
You made the statement that you twisted all the whites and pigtailed it to whatI am not an electrician. I do have experience with this and running basic outlets, wiring, etc. from the Army.
Polarity isn't crossed. Somehow the problem originated upstream from the outlets I was working on. I now have a "jumper" cable hooked up between outlet 1 & 2, as well as the original wiring hooked up as normal and it works now through the whole circuit.
Colorado is it possible that you have your switch leg crossed ?You made the statement that you twisted all the whites and pigtailed it to what
Reply to Open Neutral Issue in the USA Electrical Forum area at ElectriciansForums.net