Discuss Origin of Ze Values... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

S

Silly Sausage

Where did the nominal/limit values of Ze for TNS and TNC/PME originate from?
I mean the values that are listed in OSG and various other publications, but why?

Does it really matter? As long as your Zs for a cct falls within the max for the protective device...
 
In short circuit a cable has to cope with currents of several times + its rating but the duration of this current is vital to the damage that may occur... if too long then the insulation and environmental protection could have its characteristics compromised .. its these well researched limits that define Zs values.... nothing to do with personal safety just protection of the installation.

Tnc/pme can be subject to circulating currents in the earthing system under fault conditions and can means an installation external to the one your on could be larger and if the supply has a fault it could use your earthing system as a route... so the earthing system has to allow for this.
 
The question was the origin of Ze values

I would have thought it was more to do with permitting the ability of an installation to stay within the maximum Zs values after final circuits are added, the difference between Tnc-s and Tns values being more to do with the integrity of the supply system and its connections

The value of a Tns seperate conductor.a lead or steel sheath, rather than the copper neutral of a Tnc-s making it more vulnerable to higher resistance than what would be expected in a Tnc-s conductor
 

Reply to Origin of Ze Values... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Cable calcs using cable calc app Working out cable size for a workshop. 100m long, 100a supply, mccb 100a zs- 0.23 ohms, in a duct on its own...
Replies
2
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Just thought I'd share this quick sobering story that happened to me a couple of weekends ago.... Overhead 230v lighting festoon, LED golf ball...
Replies
5
Views
766
Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
454
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock