Discuss Oustide sockets and a new hot tub in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
362
Was just arranging to install a 2g IP socket for a customer tomorrow and now he tells me its for a hot tub!

Apparently hot tub is supplied with a 13A plug! But still trying to get some details on that!

If this is correct do I just install the sockets and not consider what ever he wants to plug into them or should I do more investigations?

Supply is TNC-S (probably)
 
Surely, if hot tub is a fixed appliance, that comes pre-wired on a 13 amp plug top, then just install suitably IP rated outdoor socket that meets the current and over current demands as well as meeting the requirements for extra protection then all is well?
 
A few questions which require confirmation,
1)Is supply PME
2)Is Hot tub Class 2 or Class 1
3)Where is hot tub to be sited in relation to general earth mass of earth etc.
4)What are manufacturers recommendations.

Am installing wiring to one myself in very near future and trying to obtain information from suppliers impossible ?. The only information so far is 32A Supply and the house supply is PME. Will wire this as TT with DP 30mA rcd protection and a 25 mtr * 3mm * 25mm earth tape in same trench as sub main. Hot tub 20 metres down garden.
 
Right I'm a bit confused here, not usually difficult. Are we to make a distinction between a proper hot tub that needs its own dedicated supply and is subject to special locations regs, and the blow up types that come with a 13A RCD plug fitted? In the absence of manufacturers detailed installation instructions are we supposed to assume that because it has a plug fitted and the user can presumably plug it into any existing outside socket that it is not subject to section 702? I can't see the difference myself, other than the blow up ones have no metallic parts so there is no possibility of any difference in earth potential or loss of neutral etc
 
Was just arranging to install a 2g IP socket for a customer tomorrow and now he tells me its for a hot tub!

Apparently hot tub is supplied with a 13A plug! But still trying to get some details on that!

If this is correct do I just install the sockets and not consider what ever he wants to plug into them or should I do more investigations?

Supply is TNC-S (probably)

What Tel said, soooorry what Trev said lol
 
As Buckfast has found out himself, there is a bit more involved with an installation of a Hot Tub or Spa than just plugging into a suitable outlet.
 
exactly-so why do these inflatable ones come with a 13A plug on them?

Pass, never seen them to be honest!! Don't sound too clever though do they!! ...lol!!

EDIT... Just had a look at the link to the ARGOS site. Seems that the heater and air pump is contained in a separate module. All looks very cheap and nasty, as you would expect for just 500 notes when the real thing is more like 5000 Quid!! lol Looked at another unit that they are calling plug and play with a 13A plug top, ....all i can say, is that with a 2 KW heater (to heat up almost 900 litres of water lol!!) and a 4 HP air blower motor they won't be able to run both at the same time, which for an almost 5K Spa isn't really acceptable...


I'd want to see some manufacturers written assurances that other UK safety wiring/installation methods are not applicable to these so called plug and play hot tubs/spa's....
 
Last edited by a moderator:
Pass, never seen them to be honest!! Don't sound too clever though do they!! ...lol!!
No that's what I thought! I got asked to look at one and decided not to bother. It came with an RCD type 13A plug and upon further investigation had no earth, so obviously class 2, but it just seemed like a bit of a pile of ---- to me. No idea where it came from as customer had bought it off Ebay.........
 
760 Liters of water. 2kW heater. Only takes 8.85 hours to warm the water from 10 deg C to 30 deg C....
 
I'm not saying they are OK, cos they look rubbish to me, but the time taken to warm them up is not really an issue cos you have to keep them on all the time apparently. BUT the issue still remains, are we to treat ANY of these things as a special location, or are they (the blow up ones) class 2 and somehow exempt?
 
Ok, just to keep everyone informed:

House supply is PME and hot tub supply needs to be 32A.

Spoke to suppliers and they say use 6mm 3core 32A/30mA protection, they didn't know anything about earthing systems.

Spoke to Elecsa technical support and they say treat it as a swimming pool (Section 702) and recommend to TT the supply from the Isolator.

Trouble I have now is that this is on a terraced house, hot tub is being placed directly beside the back door. Door is in the middle of the house and on the other side of the door is an external oil fired boiler which is obviously fed from the house and PME earthed/bonded.

Technical support reckon that if the boiler is out of reach of anyone in the hot tub that would be OK - different earthing systems. Just got to find a place for the isolator in zone 2, or it looks like I'm allowed to position an isolator 1.25m from zone 0 if zone 2 is not practicable (702.53)
 
If its so close to the house is there really likely to be a significant PD between the 2 earthing systems??? As an off the wall late at nights comment what about putting a rod down next to the tub and connecting it to the MET?? Are Elecsa only worried about differing earth potentials?
 
This thread can open a large can of worms ?. PME used for external supplies can cause problems if the neutral supply conductor becomes open circuit as all cpc conductors could rise to mains potential and supplied equipment is outside equipotential bonding zone. Some argue this is very unlikely to happen, but i would disagree with this and locality and supply arrangements need to be looked at. IE are supply cables from overhead network etc. Will DNO accept PME supplied to hot tub. Would connect this as TT and try to make sure boiler is at least 2 metres from hot tub (Extended arms reach). Potential difference between 2 earthing systems depends on locality of last DNO earth spike. Could be 20 feet away or could be 1/4 of a mile away?. If you do decide to tie PME down with earth spike make sure earth rod installation has very low impedance to be able to withstand fault currents. (Not a path i would take for hot tub installation).
 
Last edited:
Some argue this is very unlikely to happen, but i would disagree with this and locality and supply arrangements need to be looked at. IE are supply cables from overhead network etc.

Rare enough that the vast majority of electricians will never see this happen throughout their working life!! If the PME supply is from an overhead DNO supply, then this will be a ''TRUE'' PME installation with N-E connections at every third post. The more N-E connections there are on a PME distribution supply cable the less effect a broken neutral will have.

But i will agree with you that in most cases where hot tubs and the like are sitting on bare ground, concrete or other potentially conductive material, i too would TT the installation, but not with one of those worthless short thin twigs you lot in the UK call an earth rod!! lol!!
 

Reply to Oustide sockets and a new hot tub in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
644
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
232
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock