247
I know the guide states a supply to outbuildings should come via a MCB,but, if the MCB is on a RCD rail and that MCB supplies the outbuilding CU via a main switch,RCD,MCB, is that not a whole lot of gubbins that realy is not required, can the supply out not be taken direcly from the switched side of the parent CU main switch, in fact would it not serve better if the supply out was take from a couple of henlys before the parent CU.
Pict
 
Cheers, this is project I have been asked to look at,Its' a PME, with 2 outbuildings and a static caravan,1 is a propagator,2 is a chill room, and the van all are fedd from a single 100A supply but at present there is a lot of nuisance tripping mainley I think when the chill room compressor draws start up current due in part to the lack of discrimination between RCD's, this I can sort but while I am at it I would like to split the load up better that is I thought that if I split it at a point prior to the parent CU and segregate it into 3 smaller CU's within the main building the cable run is 20 metres so VD is well within limits I was wondering if this solution had merit.
Pict
 
and note that the caravan must be dissociated from the PME earth and have it's own TT system ( earth rod.).
 
Ah yes now I had not considered that at this stage thanks for jogging my memory, thankfully it should be ok with one as the ground is wet and deep, I remember one I tried to put in for a van in a wooded area, scots pin and fir thirsty beggers, the ground was dry as the dessert and as soon as the rod went through the roots it literaly disappeared never ever got it back ,
Pict
 

Reply to out building supplly in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock