Discuss out building supplly in the Australia area at ElectriciansForums.net

the pict

-
Mentor
Reaction score
247
I know the guide states a supply to outbuildings should come via a MCB,but, if the MCB is on a RCD rail and that MCB supplies the outbuilding CU via a main switch,RCD,MCB, is that not a whole lot of gubbins that realy is not required, can the supply out not be taken direcly from the switched side of the parent CU main switch, in fact would it not serve better if the supply out was take from a couple of henlys before the parent CU.
Pict
 
Cheers, this is project I have been asked to look at,Its' a PME, with 2 outbuildings and a static caravan,1 is a propagator,2 is a chill room, and the van all are fedd from a single 100A supply but at present there is a lot of nuisance tripping mainley I think when the chill room compressor draws start up current due in part to the lack of discrimination between RCD's, this I can sort but while I am at it I would like to split the load up better that is I thought that if I split it at a point prior to the parent CU and segregate it into 3 smaller CU's within the main building the cable run is 20 metres so VD is well within limits I was wondering if this solution had merit.
Pict
 
and note that the caravan must be dissociated from the PME earth and have it's own TT system ( earth rod.).
 
Ah yes now I had not considered that at this stage thanks for jogging my memory, thankfully it should be ok with one as the ground is wet and deep, I remember one I tried to put in for a van in a wooded area, scots pin and fir thirsty beggers, the ground was dry as the dessert and as soon as the rod went through the roots it literaly disappeared never ever got it back ,
Pict
 

Reply to out building supplly in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
879
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
914
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top