11
Hi,

I am currently having my whole house renovated and I am also having a new outhouse built (brick/block cavity wall etc..). We want to put a small kitchen in the outhouse and so will need to run Gas and Electric etc... We will also be putting the boiler and unvented cylinder in the outhouse.

I already know about the trench requirements etc... I would like to know about cable, consumer unit requirements.

I wont be doing any of the work my self and will be bringing a qualified electrician, but I like to know the best approach with these things, which why I am here.

I have read you can spur off the original house CU, as long as you use the side that is not connected to the RCD? Is that even the case when having a oven etc... ? I understand the CU in the house will have it's own RCD so that should cover it, just wanted confirmation?

Also in regards to cable its about 20m (max) from the outhouse to where the current house consumer unit (main fuse) is. What thickness armored cable would be recommend?

We will most likely have to upgrade the existing consumer unit as we are also building a extension and building a dormer and there aren't enough mcb's in the current unit, what would be the recommendation for the size of unit?

The house will be (after extending) 5 Bed, 2 Bath, 2 Reception, a WC, Kitchen then outhouse with another small kitchen (with the boiler and cylinder).

I hope I have provided enough information.

Appreciate any advice given.
 
Hi,

I am currently having my whole house renovated and I am also having a new outhouse built (brick/block cavity wall etc..). We want to put a small kitchen in the outhouse and so will need to run Gas and Electric etc... We will also be putting the boiler and unvented cylinder in the outhouse.

I already know about the trench requirements etc... I would like to know about cable, consumer unit requirements.

I wont be doing any of the work my self and will be bringing a qualified electrician, but I like to know the best approach with these things, which why I am here.

I have read you can spur off the original house CU, as long as you use the side that is not connected to the RCD? Is that even the case when having a oven etc... ? I understand the CU in the house will have it's own RCD so that should cover it, just wanted confirmation?

Also in regards to cable its about 20m (max) from the outhouse to where the current house consumer unit (main fuse) is. What thickness armored cable would be recommend?

We will most likely have to upgrade the existing consumer unit as we are also building a extension and building a dormer and there aren't enough mcb's in the current unit, what would be the recommendation for the size of unit?

The house will be (after extending) 5 Bed, 2 Bath, 2 Reception, a WC, Kitchen then outhouse with another small kitchen (with the boiler and cylinder).

I hope I have provided enough information.

Appreciate any advice given.
Sorry there is no where near enough information. The best advice any one could give is to get your electrician involved now at design stage. One thing I will say is you would be better with a switch fuse for the distribution circuit for selectivity.
 
As you said you are employing an electrician to do the work so they will be designing it. The cable size will depend upon many factors including load allowing for diversity (not all loads on together) As for consumer unit size this will depend on what existing circuits you have and additional new ones but the best option would be all RCBO's
 
I'm also with the above posts. Have a word with the electrician who will be installing and testing the circuit to the outhouse. He/she will tell you what is best.

We will most likely have to upgrade the existing consumer unit as we are also building a extension and building a dormer and there aren't enough mcb's in the current unit, what would be the recommendation for the size of unit?

One option is, add an extra CU next to the existing one. This way you are not touching the existing CU. This will save money. Again, have a word with the electrician. He/she will advice on this.
 
Not sure I agree with that ... the whole house is being renovated and extended ..

True mate but it sounds like the OP is not touching the existing wiring. I may have misread it... Maybe the OP can clarify please.
There are may ways to skin a cat.. I suggested one... :)
 
Just wondering why the customer needs quite so much detail about the install...

Could be that the OP is intending to do the job himself or that he is just curious as to what is needed.
If the OP is actually "bringing a qualified electrician" to do the work then they need to have a word with the electrician about the best way to do this and what is needed. After all, the electrician will be putting their name down on the cert and notifying the relevant authorities.
 
Too many specific questions from the OP. And why don't they ask the spark who will be doing it?

Answers on a postcard (not you Murdoch)
 
Thank you for the replies.

Couple of points for clarity.

I appreciate an electrician will provide this information, however when you call an electrician, you can end up getting a lot of cowboys, so its good to make sure you have a reasonable understanding of what is required rather then assume all electricians are equal :) - Plus I have OCD :)

PS: Yes the whole house being renovated, new electrics, new plumbing, new plaster, new ceilings etc....

PS2: Yes the system boiler and the cylinder will be in the outhouse, I have spoken to three four plumbers about this and this should be fine. The pipe will be run underground (1m in depth and fully insulated).

Anyway, I managed to get hold of a friend of friend (who is a fully qualified electrician - just too busy to do the job) and went through what I am planning to have done he recommended the following:

He said to take the direct feed from the meter into a new henly blocks. The henly blocks will supply main home CU and the outhouse CU. A 16mm armored cable will be run from the henly to the outhouse CU.

He recommended 16mm, as I will have boiler and kitchen (oven, microwave) in the outhouse.

I spoke to a few other electricians some said I could get away with 10mm but... most said stick with 16mm to be safe.
 
I wont be doing any of the work my self and will be bringing a qualified electrician

Anyway, I managed to get hold of a friend of friend (who is a fully qualified electrician - just too busy to do the job)

So, who is doing this work?
Shouldn't you be talking to the electrician who will actually be doing the job?
 
So, who is doing this work?
Shouldn't you be talking to the electrician who will actually be doing the job?

So the builders has finally bought in a electrician to do the job as the trenches have just finished being dug out. The electrician will be doing all the work. I asked him about the setup as well and he basically gave me a few options and one of those was what I wrote above.

Hilarious stuff this. The OP should write sitcoms.
Not sure what is so funny. Just curious about how all this would work, the answers I was getting back on this forum was ask the electrician (who wasn't around at the time), so I thought I would ask here considering that's the point of this forum?

I am guessing people probably take it as free advice or think I might be crazy and do the install my self.

Anyway I am sorted now.
 
So the builders has finally bought in a electrician to do the job as the trenches have just finished being dug out. The electrician will be doing all the work. I asked him about the setup as well and he basically gave me a few options and one of those was what I wrote above.

Who is doing the rewire then?

Sounds fishy
 
why would ANYBODY put the boiler in a separate building 20 meters away? That just sounds so odd.

I thought this at first too, however someone on our road this this as well (5 houses down) went to speak to them about it, and so far so good. Nothing major bills wise and they don't need to worry about using up space within the house for the cylinder etc.. One other benefit is the the plumbers are happy because they have really easy access to boiler and cylinder, normally when they are inside the house they are housed in cupboards etc... which can be a pain.

Who is doing the rewire then?

Sounds fishy
Builder bought in his own electrician who will do the wiring. However I am up for bringing in my own person? anyone here want a job, rewire whole house and the new outhouse.

Would it be cynical to suggest the OP and builder are one and the same? Of course it would be, perish the thought. Builders never do electrics...….do they?

LOL I work in IT, don't do any building work, getting loft, extension and new outhouse, etc.... just want a good and above board job done, so asking question. You guys are way to suspicious.

As I said, send me a pm and ill be happy for you to come down and quote me. I live in the East London area so you have an idea of where you would have to come to.
 
Would it be cynical to suggest the OP and builder are one and the same? Of course it would be, perish the thought. Builders never do electrics...….do they?

Almost, Mrs does a lot of baking on the side (she is thinking of starting a business etc..) Since we are having gas, electric and water running to the outhouse, we thought it would make sense to make a kitchen for possible future venture there, that's all.
 
Just thought I'd end the conversation here. Thank you all for responding.

As I said, happy to get alternative quotes, if you can send me a PM ill give you the details.

5 Bed
2 Bath
2 Receptions
a WC
Extension (Kitchen)
Outhouse (Boiler/Cylinder and Kitchen)

All new wiring for main house and new sockets, light switches, light fixtures.
New CU for main house
New CU for outhouse

It's a big job. The house is completely gutted now, so no need to worry about wiring runs (should be easier). The ground floor has a crawl space about 3ft and enough of the floor boards off to make wiring runs easier there.

All plaster is off the wall, and ill have the builder do any chasing etc...
 
Just thought I'd end the conversation here. Thank you all for responding.

As I said, happy to get alternative quotes, if you can send me a PM ill give you the details.

5 Bed
2 Bath
2 Receptions
a WC
Extension (Kitchen)
Outhouse (Boiler/Cylinder and Kitchen)

All new wiring for main house and new sockets, light switches, light fixtures.
New CU for main house
New CU for outhouse

It's a big job. The house is completely gutted now, so no need to worry about wiring runs (should be easier). The ground floor has a crawl space about 3ft and enough of the floor boards off to make wiring runs easier there.

All plaster is off the wall, and ill have the builder do any chasing etc...
With the job that far advanced it's leaving it a little late to engage an electrician, doesnt sound like a great deal of forward planning is in place.
 

Reply to Outhouse Consumer Unit and Underground Cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
878
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
798
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
767
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock