I've just spent an hour getting bogged down with the maths trying to work out diversity for 2 cooking appliances on the same circuit (32A MCB) and same isolation switch,

I thought I would give my workings so others can use it as I wonder if some just assume you can still use the 15kW maximum, which you can't.

In fact the the maximum for 1 cooking appliance seems to be 19.3kW (as long as the switch doesn't incorporate a socket), however, on with 2 appliances....

Diversity is 10A plus 30% of the remaining amps (plus 5A if a socket) but this is for each appliance even if on the same circuit.

Therefore for an oven and electric hob the maximum current we have is:

[10A + ( 0.3 x Q) ] + [10A + (0.3 x Q) ] = 32A

we don't know the maximum size of the cooker and hob (that's what we're trying to find out), so I have just used the letter Q (Q is the current of either the hob or cooker minus the 10A)

Therefore

The above equation is the same as

2 x (10A + 0.3Q) = 32A

20A + 0.6Q = 32A

0.6Q = 12A

Q = 20A

We know that each appliance is allowed to draw a max current of Q +10A, which is 30A. There are 2 of them so 60A.

60A x 230w = 13.8kW (approx)

Therefore maximum combined power for 2 appliances on same circuit with same switch (without a single socket) is 13.8kW.

I think you'll all have had enough now, but the maths works out as a maximum combined power of 10.4kW allowed if the cooker switch incorporates a single socket. (Equation is 25A + 0.6Q = 32A)

If you haven't guessed. I have the day off work! ?

ps.. would you check the maths please @happysteve
 
Your numbers are correct but it is important not to overlook the significance of the 10A + 30% of remainder, otherwise you might end up following the letter of the regulations but missing their intention.

A single, self-contained cooker might offer the same functionality as an oven and a hob as two separate appliances. Assuming similar efficiency, the current consumption of any appliance to cook a given meal will be similar, i.e. it is the cooking activity that governs the load, not the layout of the rings and ovens. It would be weird then to say that 32A Ib is adequate to support the oven and hob of a cooker cooking as much as one can reasonably cook, but you need 40% more current if they are mounted separately into the kitchen units.

The glitch is that 10A. By splitting the appliance in half, a second baseline load of 10A has been allocated that is considered to be switched on all the time, that does not correspond to any extra cooking activity or elements.

Discuss.
 
Hi - I haven’t got my head around the calcs yet, but using OSG Table A2 line entry 3 Cooking Appliances, I get interpret the load after diversity as -
10 + 0.3*(FL Oven + FL Hob -10)

If I’ve understood correctly, this reflects LN’s point about not having a 2nd 10A allocation since it’s still one domestic kitchen.
 
I can see what you mean Lucien. It doesn't make any sense to treat a combined oven and hob differently to a separate oven and hob as they will both be used the same (I think). However, I think you would still have treat the diversity as separate for both of them as the OSG specifically says 'individual' household installations.

The regulations can't cater for every single eventuality, so sometimes they don't quite make sense, but I don't think that is a reason to make your own judgement to change them as you do not have underlying knowledge of the calculations used to form them and you are choosing to change them based on the fact you think you are right. If you do change them, then at some point, perhaps 1 in a thousand, a problem will occur, whereas if you stuck to the regs it wouldn't. Of course, you may be right ?.

It's difficult to think of an example but perhaps if the combined oven and hob is changed for a standard oven and a hugely powered induction hob.
 
The regulations can't cater for every single eventuality, so sometimes they don't quite make sense,

Although not perfect, they usually make sense if applied appropriately, even if they don't specifically deal with the situation being considered. They are a design standard, not an instruction manual.

I don't think that is a reason to make your own judgement to change them as you do not have underlying knowledge of the calculations used to form them and you are choosing to change them based on the fact you think you are right

Would you prefer to follow a procedure that appears incorrect for a situation, or one that is more correct based on the laws of physics for which you have to accept responsibility?

As it happens, I cannot quote BS7671 verbatim on the subject of domestic cooker diversity, beyond 10A +30%. I've never installed a cooker and I don't do domestic work, so it's not high on my priorities list. But my laws of physics are the same ones that electricity follows, I know how thermostats and simmerstats and induction hobs work and the thermal characteristics of heating elements, ovens, pans of water etc, and enough about cooking to understand how the appliances are used in practice. So it wouldn't bother me very much to make my own assessment if I needed to.

perhaps if the combined oven and hob is changed for a standard oven and a hugely powered induction hob.

In that case you are changing the connected load, not the diversity calculation. Using the 10A + 30% rule, increasing the connected load will increase Ib but not in proportion, which is reasonable and that is what diversity is all about. Hence the idea of base load plus a fraction of the remainder, rather than a larger fraction of the total.

Cooker physics homework: Show that a large element working at low duty-cycle will cause a greater temperature rise in a given supply cable than a smaller element working at a higher duty-cycle delivering the same mean heat output. Assume that the voltage drop in the cable is a small fraction of the supply voltage and that the thermal time-constant of the cable is much greater than the period of the duty-cycle controller.


E2A my first sentence was badly phrased and I have changed it. I did not mean to imply that you personally might not intelligently apply the regs, rather the opposite.
 
Last edited:
Would you prefer to follow a procedure that appears incorrect for a situation, or one that is more correct based on the laws of physics for which you have to accept responsibility?
If a procedure was clearly wrong then no, you wouldn't follow it, but in this case I don't think it's clearly wrong. I think it may be right, although I'm not sure. I'll expand on my example......
In that case you are changing the connected load, not the diversity calculation. Using the 10A + 30% rule, increasing the connected load will increase Ib but not in proportion, which is reasonable and that is what diversity is all about. Hence the idea of base load plus a fraction of the remainder, rather than a larger fraction of the total.
example expanded.....

The diversity applies to 'individual' cooking appliances. I'm not sure if there are single cooking appliances that contain a fairly low powered oven with a huge high powered induction hob. Therefore that type of cooking appliance would not have been catered for when working out the diversity calculation.

Also, would it make a difference how far apart they were (and still on the same circuit). If one was in a different room would you still feel they should be classed as one appliance? My point is that we'll have to make a judgement, and I wonder if the OSG diversity for cooking appliances is trying to avoid you making this judgement and just give a blanket calculation to avoid, or minimise the chance of overload.
 
Although not perfect, they usually make sense if applied appropriately, even if they don't specifically deal with the situation being considered. They are a design standard, not an instruction manual.



Would you prefer to follow a procedure that appears incorrect for a situation, or one that is more correct based on the laws of physics for which you have to accept responsibility?

As it happens, I cannot quote BS7671 verbatim on the subject of domestic cooker diversity, beyond 10A +30%. I've never installed a cooker and I don't do domestic work, so it's not high on my priorities list. But my laws of physics are the same ones that electricity follows, I know how thermostats and simmerstats and induction hobs work and the thermal characteristics of heating elements, ovens, pans of water etc, and enough about cooking to understand how the appliances are used in practice. So it wouldn't bother me very much to make my own assessment if I needed to.



In that case you are changing the connected load, not the diversity calculation. Using the 10A + 30% rule, increasing the connected load will increase Ib but not in proportion, which is reasonable and that is what diversity is all about. Hence the idea of base load plus a fraction of the remainder, rather than a larger fraction of the total.

Cooker physics homework: Show that a large element working at low duty-cycle will cause a greater temperature rise in a given supply cable than a smaller element working at a higher duty-cycle delivering the same mean heat output. Assume that the voltage drop in the cable is a small fraction of the supply voltage and that the thermal time-constant of the cable is much greater than the period of the duty-cycle controller.


E2A my first sentence was badly phrased and I have changed it. I did not mean to imply that you personally might not intelligently apply the regs, rather the opposite.
Would I be correct in concluding you are in agreement with using the principle of "Common sense" though the regs may not refer to it specifically?
 
Reductio ad absurdum: If a 4-ring hob were divided into single hotplates each connected to an FCU and you treated them as separate appliances, you would have to allow over 40A for the hob alone, whereas 32A is sufficient for an entire cooker including the oven and grill.

Notwithstanding the issue dealt with in my homework question, a high-powered hob won't use much more power to cook the same meal as a low-powered one. Yes, you can cook more, not least because you can bring things to the boil faster etc, so there is a likelihood that more current will be used and this is reflected in the diversity equation.

A hob of 9.2kW connected load comes to 19A with diversity, one of 13.8kW comes to 25A. More current, because the hob can heat stuff more quickly, but not 50% more because it is very unlikely for all the extra available heat to be utilised by normal cookery.

If one was in a different room would you still feel they should be classed as one appliance?

No, because that would suggest that the manner of usage might be different. I am not arguing that cooking appliances in different rooms would count as one appliance simply because they share a circuit. Clearly, one person might be cooking a full meal on one and another person doing the same in the other room. I am arguing that the same elements fulfilling the same purposes as those of a single, conventional cooker in a domestic kitchen, will take approximately the same current even if they are physically arranged as two separate boxes, and therefore it is rather arbitrary to insist on using a different method to calculate their total design load.

Amongst the possible incidental relationships between appliance configuration and current that I considered, was that a user with more advanced cookery skills might both specify 'better' appliances and also use more current by being a more streamlined cook working with a greater number of dishes at once. But BS7671 does not rate appliances by 'goodness', only by loading, and if they specify a larger appliance then the design current will indeed be higher after diversity. FWIW a 'better' oven might have better thermal insulation, in which case it will use less current to cook the same meal, or might be bigger without using more current.
 
most of the time not all elements will be on unless the chef is in a hurry.
With the new A rated appliance now in.
EU gistappo made up a rule trying to dicarage us from using so much power.
So us brits can go to work on a egg. Lol
 
So long as the MCB provides overload protection for the cable, I would side with Lucian and say use the 10A + 30% of remainder of the combined appliances load as it is essentially one cooking station.

Even with a single cooker you can turn everything to max and draw the rated power and so exceed the diversity calcs, it is just no sane chef would be doing that...
 
Even with a single cooker you can turn everything to max and draw the rated power and so exceed the diversity calcs, it is just no sane chef would be doing that...

Only time it happens is right after I've installed a new cooker/hob, when I turn everything on full for a while to burn all the elements clean and get rid of the smoke and smell before handing over.
 
Well It looks like the consensus is my time consuming, brilliantly formed maths is correct but of absolutely no use ?. Still I enjoyed working it out!

I've just been working on another equation for excel to work out my average yearly interest rate over the past 10 years. took about 30 mins to realise I need to use nth root in the equation. I do love maths!

Thanks for the discussion and insight to all who replied, especially @Lucien Nunes for his usual intelligent and in depth explanations.
 
HHD I know you are always keen to analyse and get to the bottom of what's going on and I wish more people would do that, rather than relying on rules of thumb and guesswork. OK, in this case I wasn't in agreement that your method was an accurate model but it prompted some discussion and comparing of theory and practice and I think that is often lacking. People do stuff on paper to pass exams, and then nail stuff to the wall, but don't make enough of a connection between them. IMO the real trick is not to get too fixated on regs, which are just the particular locally-recognised standards that we generally work to, but rather to look at the physics that makes electrical stuff work. Heating elements obey ohm's law, not BS7671!

E2A: But, next time, please don't use Q for an unknown current. Capital Q is charge, usually in coulombs. Either x (the general unknown) or I (for current, the actual quantity that was unknown in this case) would suit. Since Q=It, using Q for current makes time disappear, which could cause wider issues with the universe.

My thought is it should be treated as one device if they are off one common isolator

I can see what you are getting at, i.e. one cooking station controlled as a unit from a single point, but referring to the isolator specifically seems arbitrary as it has no effect on how the appliances are used.
 
Last edited:
Now I understand why a 5-ring hob is better than a 4-ring hob - higher Q! They should get rid of all that resistance in the elements and it would go on for hundreds of cycles.
 
HHD I know you are always keen to analyse and get to the bottom of what's going on and I wish more people would do that, rather than relying on rules of thumb and guesswork. OK, in this case I wasn't in agreement that your method was an accurate model but it prompted some discussion and comparing of theory and practice and I think that is often lacking. People do stuff on paper to pass exams, and then nail stuff to the wall, but don't make enough of a connection between them. IMO the real trick is not to get too fixated on regs, which are just the particular locally-recognised standards that we generally work to, but rather to look at the physics that makes electrical stuff work. Heating elements obey ohm's law, not BS7671!

E2A: But, next time, please don't use Q for an unknown current. Capital Q is charge, usually in coulombs. Either x (the general unknown) or I (for current, the actual quantity that was unknown in this case) would suit. Since Q=It, using Q for current makes time disappear, which could cause wider issues with the universe.



I can see what you are getting at, i.e. one cooking station controlled as a unit from a single point, but referring to the isolator specifically seems arbitrary as it has no effect on how the appliances are used.
Haha... I first put an X in the equation, as you rightly say this is the standard letter used for a variable, but it looked like this.... 0.3 x X, I realise It should just be written 0.3X but I wanted (at least initially) to show the multiplication sign. 0.3 x I looked too much like 0.3 x 1, or with the multiplication sign removed 0.3I, now looking like 0.31.

I then used 'Y', which I think I should have stuck with. Q shall never be used again in such a form!?
 
But Y is the symbol for admittance, the reciprocal of impedance (Y=1/Z). Many capital letters stand for quantities and should not be used generally.

Its very often possible to distinguish 0.3I from 0.31 automatically by context (0.3I has dimensions of current but 0.31 is dimensionless.) However if an explicit multiplication symbol is needed to avoid ambiguity or for visual clarity, there is a choice of the asterisk * (from ASCII-based programming) or a full stop aka period or centre dot which is the conventional algebraic symbol to use on paper. Conventions that use the centre-dot for decimal fractions theoretically use the period for multiplication and vice versa. I would understand 0.3I, 0⋅3.I, 0⋅3*I etc as equivalent. In vector algebra the two multiplication operators ⋅ and x signify different operations, but again it would be clear from context that the distinction doesn't apply here.
 
I've not read through thoroughly all the replies, but when I was calculating diversity for two appliances, I would use two calculations. With one free standing, it would be one calculation.

I based my rational on that the later are sometime supplied with a plug, with very simple cooking activity and the former could have multiple zones for a hob and two or three or more zones for the oven part. Much more cooking activity.

That said, I once had a Range style electrical cooker, which had 3 ovens, manufacturer required 40A supply. With all three ovens going at full pelt, never pulled more than 14A.
 
Ours only has two ovens but with both of those on, the grill, all four rings and the lights, it uses about half an amp.
 
The burners are gas, yes, but for some reason the clock, lights and rotisserie are electric.
 
I realise we have come to the end if this thread, however.... as coincidence happens a slightly different yet similar scenario has arisen.

The customer wants 2 x separate single ovens next to each other with an induction hob above.

The previous answers in this thread suggest treating a separate hob and oven as a single appliance with regards diversity, and I can see that makes sense. We can't just keep adding an appliance on and classing it as one unit though, as single units have thermostatic controls. How would you apply diversity in this case? I'm inclined to use my initial maths here and class it as 2 appliances.
 
I realise we have come to the end if this thread, however.... as coincidence happens a slightly different yet similar scenario has arisen.

The customer wants 2 x separate single ovens next to each other with an induction hob above.

The previous answers in this thread suggest treating a separate hob and oven as a single appliance with regards diversity, and I can see that makes sense. We can't just keep adding an appliance on and classing it as one unit though, as single units have thermostatic controls. How would you apply diversity in this case? I'm inclined to use my initial maths here and class it as 2 appliances.
I didn’t agree with that concept myself; I treated individual appliances separately when apply diversity, for the reasons you’ve now been presented with.
 
This Math looks wrong to me, forgetting the incorrect use of Q,

Incorrect
2 x (10A + 0.3Q) = 32A

20A + 0.6Q = 32A

0.6Q = 12A

Q = 20A

Correct

2 x (10A + 0.3Q) = 32A

20A + 0.6Q = 32A

32A - 20A = 12A

100% of the remaining = 12A

Therefore 60% of the remaining = 7.2A

Value of Q = 7.2A

Circuit then has a 4.8A buffer

Then if you actually take into account load 32A is more than sufficient
 
This Math looks wrong to me, forgetting the incorrect use of Q,

Incorrect
2 x (10A + 0.3Q) = 32A

20A + 0.6Q = 32A

0.6Q = 12A

Q = 20A

Correct

2 x (10A + 0.3Q) = 32A

20A + 0.6Q = 32A

32A - 20A = 12A

100% of the remaining = 12A

Therefore 60% of the remaining = 7.2A

Value of Q = 7.2A

Circuit then has a 4.8A buffer

Then if you actually take into account load 32A is more than sufficient
This is wrong also though. Q is actually a known value determined by the appliance(s), the 32A is the unknown value which needs to be worked out via calculation.
 
Oh dear.

Now Lucien will see it (the ill placed and brazen )
1645571796832.png
again and get cross with me... again😫
 
The use of a comma as a separator is not unusual, and as one doesn't usually work in a bilingual situation, it seldom causes confusion. What does confuse me quite often is that the arroba key (@) is in different positions on the keyboard depending on the country you are in at the time, assuming one is using a "local" keyboard of a physical nature...but then, I am easily confused!
 

Reply to Oven and hob on same MCB and diversity. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
968
Hi all, I'm getting a 32a induction hob and a 13a oven installed as part of a kitchen refurb. The existing cooker circuit is 6mm protected by a...
Replies
7
Views
2K
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
262
Hi, we are replacing our old hob and cooker and I need a bit of help, to make sure all is safe. This is the oven and hob specs: AEG IKB64401FB...
Replies
0
Views
2K
Hi all, Recently a mate had a new kitchen fitted, he's gone for an induction hob and pyrolytic oven, no gas at the property. At 1st fix a single...
Replies
10
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock