I would say absolutely 100%, if you don't install AFDDs where they are required it's a departure and as I've outlined above, the regulations and the definition of "recommended" mean they are required in all domestic settings.

But that's just my interpretation, I'd be more than happy to be proven wrong.
Go back through the new regs. SPDs a must or wavier. AFDDs still just a bog standard recommendation with no caveat.
 
I don't have the BBB yet, but if this is what the regs actually say...

"Regulation 421.1.7 now states:

Arc fault detection devices (AFDD) conforming to
BS EN 62606 shall be provided for single-phase
AC final circuits supplying socket-outlets with a rated
current not exceeding 32 A in:

• Higher Risk Residential Buildings (HRRB)
• Houses in Multiple Occupation (HMO) i
• Purpose-built student accommodation ii
• Care homes iii

NOTE 1: Higher Risk Residential Buildings are assumed to
be residential buildings over 18 m in height or in excess of
six storeys, whichever is met first. It is anticipated that in
many areas higher risk residential buildings will be defined in
legislation which can be subject to change over time, as well
as in risk management procedures adopted by fire and rescue
services. Current legislation should be applied.

For all other premises, the use of AFDDs conforming
to BS EN 62606 is recommended for single-phase
AC final circuits supplying socket-outlets not
exceeding 32 A.


Where used, AFDDs shall be placed at the origin
of the circuit to be protected.
The use of AFDDs does not obviate the need to apply
one or more measures provided in other clauses in
BS 7671.

NOTE 2: For busbar systems conforming to BS EN 61439-6
and Powertrack systems to BS EN 61534, the AFDD may be
placed at a location other than the origin of the circuit."

Thats taken from this:-


Which also clarifies the "recommended = should".

I'd say there's no room for a choice in there.
 
So your saying all new installations, DB changes you have to install AFDDs. EICRs, what code 2/3. Your wrong. Not mandatory.
No I'm not saying that.
Read 421.1.7
Note the word "shall".
Your original generalisation was not true.
What you guessed I was saying is also not true.
 
I don't have the BBB yet, but if this is what the regs actually say...

"Regulation 421.1.7 now states:

Arc fault detection devices (AFDD) conforming to
BS EN 62606 shall be provided for single-phase
AC final circuits supplying socket-outlets with a rated
current not exceeding 32 A in:

• Higher Risk Residential Buildings (HRRB)
• Houses in Multiple Occupation (HMO) i
• Purpose-built student accommodation ii
• Care homes iii

NOTE 1: Higher Risk Residential Buildings are assumed to
be residential buildings over 18 m in height or in excess of
six storeys, whichever is met first. It is anticipated that in
many areas higher risk residential buildings will be defined in
legislation which can be subject to change over time, as well
as in risk management procedures adopted by fire and rescue
services. Current legislation should be applied.

For all other premises, the use of AFDDs conforming
to BS EN 62606 is recommended for single-phase
AC final circuits supplying socket-outlets not
exceeding 32 A.


Where used, AFDDs shall be placed at the origin
of the circuit to be protected.
The use of AFDDs does not obviate the need to apply
one or more measures provided in other clauses in
BS 7671.

NOTE 2: For busbar systems conforming to BS EN 61439-6
and Powertrack systems to BS EN 61534, the AFDD may be
placed at a location other than the origin of the circuit."

Thats taken from this:-


Which also clarifies the "recommended = should".

I'd say there's no room for a choice in there.
Wow. Sorry dude. Need to look more into that. Need to see if we're just looking at new builds. And 18m is pretty high. I do mainly EICRS so need to see where this sits. Again, apologie🙏
 
Which also clarifies the "recommended = should".
I would take that clarification with a ton of salt.

Page 18 of the new regs book has a little table. The 2nd column should be the first column, as the intent is to translate the verbal form in BS7671 to an implication.
It says "Shall" is a requirement and normative, and "Should" is a recommendation (and is not normative)

If one studies the definitions on page 18 of Guidance, Normative Element, Requirement, and Recommendation I cannot see how anyone would conclude:

There is a misleading view being communicated within the industry that use of such terms as ‘recommended’, ‘additional’ and ‘specified’ demotes the requirements within the associated regulations.

In particular, Recommendation is ONE possibility and does not exclude other possibilities (including doing nothing)
 

Reply to Oven Replacement - RCD? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
926
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
D
Hi, I've searched these forums and have found quite a bit of good information, but not specifically to my query. My house is about 9 years old...
Replies
2
Views
2K
Morning guys, I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock