I don't have the BBB yet, but if this is what the regs actually say...
"Regulation 421.1.7 now states:
Arc fault detection devices (AFDD) conforming to
BS EN 62606 shall be provided for single-phase
AC final circuits supplying socket-outlets with a rated
current not exceeding 32 A in:
• Higher Risk Residential Buildings (HRRB)
• Houses in Multiple Occupation (HMO) i
• Purpose-built student accommodation ii
• Care homes iii
NOTE 1: Higher Risk Residential Buildings are assumed to
be residential buildings over 18 m in height or in excess of
six storeys, whichever is met first. It is anticipated that in
many areas higher risk residential buildings will be defined in
legislation which can be subject to change over time, as well
as in risk management procedures adopted by fire and rescue
services. Current legislation should be applied.
For all other premises, the use of AFDDs conforming
to BS EN 62606 is recommended for single-phase
AC final circuits supplying socket-outlets not
exceeding 32 A.
Where used, AFDDs shall be placed at the origin
of the circuit to be protected.
The use of AFDDs does not obviate the need to apply
one or more measures provided in other clauses in
BS 7671.
NOTE 2: For busbar systems conforming to BS EN 61439-6
and Powertrack systems to BS EN 61534, the AFDD may be
placed at a location other than the origin of the circuit."
Thats taken from this:-
Which also clarifies the "recommended = should".
I'd say there's no room for a choice in there.