If one studies the definitions on page 18 of Guidance, Normative Element, Requirement, and Recommendation I cannot see how anyone would conclude:

I suspect if one's interests were heavily invested in the sale of associated goods, then it would be very easy to reach such a conclusion.

Is a trade association wilfully misrepresenting BS7671? I couldn't possibly speculate.
 
I would take that clarification with a ton of salt.

Page 18 of the new regs book has a little table. The 2nd column should be the first column, as the intent is to translate the verbal form in BS7671 to an implication.
It says "Shall" is a requirement and normative, and "Should" is a recommendation (and is not normative)

If one studies the definitions on page 18 of Guidance, Normative Element, Requirement, and Recommendation I cannot see how anyone would conclude:

There is a misleading view being communicated within the industry that use of such terms as ‘recommended’, ‘additional’ and ‘specified’ demotes the requirements within the associated regulations.

In particular, Recommendation is ONE possibility and does not exclude other possibilities (including doing nothing)

Excellent! I knew I'd seen that somewhere
It has to be the case, otherwise the requirements for where AFDDs are fitted wouldn't make sense in the way they are split.
 
I would take that clarification with a ton of salt.

Page 18 of the new regs book has a little table. The 2nd column should be the first column, as the intent is to translate the verbal form in BS7671 to an implication.
It says "Shall" is a requirement and normative, and "Should" is a recommendation (and is not normative)

If one studies the definitions on page 18 of Guidance, Normative Element, Requirement, and Recommendation I cannot see how anyone would conclude:

There is a misleading view being communicated within the industry that use of such terms as ‘recommended’, ‘additional’ and ‘specified’ demotes the requirements within the associated regulations.

In particular, Recommendation is ONE possibility and does not exclude other possibilities (including doing nothing)
Nice one Tim! So it's the word 'should' that has been defined, rather than the word 'recommend'? Ok, now it's starting to make sense! 👍
 
Nice one Tim! So it's the word 'should' that has been defined, rather than the word 'recommend'? Ok, now it's starting to make sense! 👍
The more you look into this, the more daft it gets.
Here's the table in BS7671:
1668715333841.png


Note the bit at the bottom.
Now, if we look at that joyous publication, it contains this table, the ancestor.
1668715389250.png


For a completely inexplicable reason some nitwit thought it made sense to invert the first two columns in BS7671. The only bit that adds clarity is that "Should" is always "Informative" in BS7671.

The BSI document also says:
1668715622639.png


So yes, the only way this makes any sense is if "should" is the thing being defined, which is how the drafting standard which BS7671 aspires to comply with has it.
 

Attachments

  • 1668715531693.png
    37.8 KB · Views: 2
I'm employed directly by the organisation. Not a contractor, actual payroll. I've spent 3 nights thinking about this. Going by my salary thats over £345 worth of thinking hours. I proceeded to buy £360 of MR30 pods from Willrose in the end. I slept better for it. (Cue the argument about fitting used goods. They come tested, I retested them and all was fine and noted it on the cert. What more can you do other than replace an entire board). Ultimately as above, it's a bit of a **** situation on BSI's part. But I've gone above and beyond in making it safer than I found it if nothing else.
 
I'm employed directly by the organisation. Not a contractor, actual payroll. I've spent 3 nights thinking about this. Going by my salary thats over £345 worth of thinking hours. I proceeded to buy £360 of MR30 pods from Willrose in the end. I slept better for it. (Cue the argument about fitting used goods. They come tested, I retested them and all was fine and noted it on the cert. What more can you do other than replace an entire board). Ultimately as above, it's a bit of a **** situation on BSI's part. But I've gone above and beyond in making it safer than I found it if nothing else.
You have followed the manufacturers recommendation, and no one could/shall/should (!) shoot you down for doing so!
 
So thinking above oven elements….and I’m definitely over thinking here….
An rcd tripping is fairly common if an element is on its way out.
If the failure mode is leakage to earth, is it fair to assume that if there was no RCD this could degrade over time, and the fault resistance could get low enough to make the cooker a bit tingly to the touch but not super-low enough to trip an over current device.
Or does it tend to end up open circuit before that happens?
I’m just wondering how this played out before we had RCDs.
 
So thinking above oven elements….and I’m definitely over thinking here….
An rcd tripping is fairly common if an element is on its way out.
If the failure mode is leakage to earth, is it fair to assume that if there was no RCD this could degrade over time, and the fault resistance could get low enough to make the cooker a bit tingly to the touch but not super-low enough to trip an over current device.
Or does it tend to end up open circuit before that happens?
I’m just wondering how this played out before we had RCDs.
I can't think of one that I've seen that was tripping breaker/fuse.
I guess it depends on where the element fails and if that element touches the casing.
 
I am a specifier, who employs electricians, and I am familiar with the regs. My actual background is lawyer. Perhaps professionals are looking at this (including AFDDs) the wrong way.

What I say to myself is "the manufacturer has recommended this, it is also strongly advised (at the least) in the regulations, therefore best practice and the most defensible position is to fit the device". If for any reason there is an accident or fire, the judge would want to know precisely why you ignored recommendations or regulatory guidance, and how you communicated and documented that, and how you mitigated the risks. If ever it got to court, you could be certain that the other side (insurance company barrister probably) would have an expert on hand to say that failure to follow recommendations is negligent. They would pay little heed to semantic discussions along the lines of "recommended means optional".

In our developments we fit AFDDs to socket circuits now as a matter of course, and in the example above where these are domestic ovens with an explicit manufactured recommendation of an RCD, I would specify that too. It is much better to do this than have to mount some defence later and try to convince a court that I know better than the manufacturer of the product.

Extra cost is peanuts in the context of a development or commercial installation. I accept that domestic remedial installers may have an uphill task getting people to accept the extra costs though.
 

Reply to Oven Replacement - RCD? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
915
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
D
Hi, I've searched these forums and have found quite a bit of good information, but not specifically to my query. My house is about 9 years old...
Replies
2
Views
2K
Morning guys, I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock