hightower

Brother got his oven cleaned yesterday, today it's tripping the RCD (not the breaker) - I'm gonna head over tonight and take a look for him but just thought I'd post here and ask for advice/possible things to look for.

Thanks,
 
damp probably, or cleaner has disturbed something that was potentially a tripping issue. try IR test but leave the meter testing for a bit. see if the reading rises.
 
I would say moisture ingress into some part of the oven from the cleaning.
Last time my missus fried a bit of our oven it was from getting water down behind the knobs which shorted a knob control. A steam cleaner could possibly have pushed water into the rear through the cavity as well I suppose.
 
Oh, more information trickled in. Love that. He says oven was working once after clean, so cleaned yesterday dinner, used last night, gone to use this morning and tripping the RCD.

Asked for information of what is causing it, ie does it trip when turned on at wall, or when light it turned on, grill, fan etc. Because it's worked since it leads me to think there's simply an element of coincidence?
 
Oh, more information trickled in. Love that. He says oven was working once after clean, so cleaned yesterday dinner, used last night, gone to use this morning and tripping the RCD.

Asked for information of what is causing it, ie does it trip when turned on at wall, or when light it turned on, grill, fan etc. Because it's worked since it leads me to think there's simply an element of coincidence?

Or moisture slowly working it's way into somewhere ? Definitely don't rule out coincidence though, one of the best tools in fault finding is an open mind.
 
Okay, little more info again. The oven will happily sit with the mode select in off, and the temp select in off, and the oven on at the wall - however, the light indicating the oven is heating is on. He says whenever he turns a dial - so either the mode select or the temp select - the RCD trips. Any more thoughts?
 
Sounds like moisture to me and if so it's almost certainly a product of the cleaning.
If a complaint is to be made then disconnect the oven, test the oven circuit, and record the details to prove no fault lies with the final circuit.
 
Brother has phoned the oven cleaner and asked him to sort - he's arranged for a sparky to visit tonight which is good service I reckon. Will keep thread updated with outcome.
 
That is good service from the cleaner. I would put a little blowy heater on to see if that helps. Defo sounds like it is related to it being cleaned. I am a little surprised that no selection at all is available on the dial, I would have thought it would maybe be the bottom element selection, or whichever, which would cause the trip, rather than all of the selections. It doesn't sound like the thermostat if the little light is coming on.

I had a customer once whose RCD was tripping. Narrowed it down to the built in microwave. Then they decided to tell me they had recently tried to clean it by putting a bowl of water inside and leaving it to bubble away. They tried to basically steam clean it!
 
That is good service from the cleaner. I would put a little blowy heater on to see if that helps. Defo sounds like it is related to it being cleaned. I am a little surprised that no selection at all is available on the dial, I would have thought it would maybe be the bottom element selection, or whichever, which would cause the trip, rather than all of the selections. It doesn't sound like the thermostat if the little light is coming on.

I had a customer once whose RCD was tripping. Narrowed it down to the built in microwave. Then they decided to tell me they had recently tried to clean it by putting a bowl of water inside and leaving it to bubble away. They tried to basically steam clean it!


Morons!

Everyone knows you boil vinegar in the microwave to clean it!

(actually, that works, so long as you don't leave it too long)
 
Morons!

Everyone knows you boil vinegar in the microwave to clean it!

(actually, that works, so long as you don't leave it too long)

I actually smashed the glass plate in our microwave. Had a Google, £40 to replace the plate..... pffft, I'll just buy a new microwave for that. Google the microwave, £300 brand new. Yeah, I'll replace the plate then.

Not sure how this is relevant at all to my OP, but it's Friday so who cares.
 
The element will draw moisture from the oven and trip the rcd.
Elements are hygroscopic.
It is quite common with ovens that have stood unused too.
Drying them out usually solves the problem .
 
The element will draw moisture from the oven and trip the rcd.
Elements are hygroscopic.
It is quite common with ovens that have stood unused too.
Drying them out usually solves the problem .

Don't remind me! I had an argument with an electrical engineer over this. He was a tenant in a property and he would work away from home all the time, and his oven only got used at weekends occasionally. This was a flat that had some damp issues also. When I clamped the oven as it warmed up the meter went from 3mA up to 21mA and then tripped each time, until around the third time when it held for a while longer. Replaced the element as it was essentially faulty, but the engineer could not see my point whatsoever.
 
I have a friend who has a lot of rented properties , this problem occurs from time to time when they have stood empty for awhile.
Funny enough it is more prevalent in the free standing cookers, I suppose that is because the 'rings 'are more exposed to the humidity.
 
i meggered my hob the other day.got a reading of >299 till the gas exploded. :toilet:
 
Had another customer that wanted their 'new' oven fitted a few years back. I upended it to get to the terminals and must have been half a pint of dirty water came out. Perplexed I spoke to the customer. Turns out they got it from their brother. His house was one of the unlucky ones in the Morpeth floods a few years back, and yep, the oven was flooded too! I then suggested that Curry's would probably have some good deals on!
 
I worked in a few of those.
One insurance company would only allow the base units to be changed one of the kitchens as the top units were not damaged lol.
They had to concede in the end though.
 
Well, it seems you've done it again you bunch of legends. Told brother to direct a fan heater towards the oven for a half hour. Turned on without tripping after and he's now been running the oven for a couple hours to try and dry it out thoroughly.

Glad all sorted mate. Think I deserve some lovin tho for #9!! Cmon HT!!

Much much much more importantly though, make sure your brother cancels the spark who's coming round later. It's Friday afterall, should be going home early!!
 
Glad all sorted mate. Think I deserve some lovin tho for #9!! Cmon HT!!

Much much much more importantly though, make sure your brother cancels the spark who's coming round later. It's Friday afterall, should be going home early!!

Everyone gets some lovin. I mean, who would have though you put a bunch of misfits together on a blue and yellow webpage, and they produce something as awesome as this place.

Anyway, yeah, I've told him not to be a p**** and make sure he tells the guy. I think thanks are in order to the cleaning company too as I thought it was a pretty professional response.
 

Reply to Oven Tripping RCD Since Cleaned in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
384
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
926
Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
Replies
136
Views
14K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock