Discuss overcurrent in dc motor in the Commercial Electrical Advice area at ElectriciansForums.net

C

cranedude

Hi ,first time posting

looking for advice on a current problem we have with a rail mounted gantry crane.

2 long travel motors ( 40hp ) were found to be beyond repair recently..we changed both and carried out a stall test ...i found the current values exceed far beyond normal working and this no doubt is the initial cause of the motors failing.

These 2 motors are in parallel with a balancing cable between the interpole coils and armature connections to keep the motors running at the same speed due to rail irregularities...fields are kept consistent..with voltage changing from the generator/resistance circuit feeding the armatures...there are also ballast resistors to absorb the heat.

variable voltage is from a ward Leonard generator with the speed control changed with resistance changing as demanded.

All resistances are of the correct value....and check out for I/R faults.also cables are not earthed/shorted.

speed 1 seems ok..however speed 2 is around 180A on both motors ( should be around 120A)..at this point we can hear the genny struggling ...speed 3 -4 is causing flashing and for the overload to trip and motion to cut out..

Any advice on where to start this fault greatly appreciated
 
Ahhh Ward Lenard systems. Dealt with a few in my time.

I'll await some more info if you can before advising.

We did have an expert on here, until he went an got banned.
 
I've given you full member permissions so feel free to post photos or circuit dwgs etc. There's a filesize limit so I'd suggest keep them < 500kb.
 
Thx Marvo.

no need to post diagrams at the moment as the dayshift came through and found the fault.

Turns out that the marking on the connections poles for A and AA were reversed ( refurbed motor)...which in turn means that the interpoles are incorrectly wired in one motor...and reversing the fields just wouldnt cut it..

The most difficult of faults oftentime have the simplest of answers..kicking myself..ha.

No doubt the ward leonard diagrams will return soon..it does often throw the odd spanner at us...this was just senilty on this occasion
 
Ahh, I doubt you'd have got you answer in this case via the forum without mentioning the fact it's just been rewound. Glad you got it sorted anyway.
 

Reply to overcurrent in dc motor in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, I need to understand whether a DC motor is sturdy or not. The support person told me to measure the armature and field winding resistance...
Replies
0
Views
453
We are in the process of restoring 4 of a group of 5 Brookhirst DC motor starters from 1936. These are a thing of beauty and the engineering in...
Replies
1
Views
1K
We have 10 energy meter in that 4x of them are giving the negative reading. The events shown are two 1is Negative Power Element 2 Warnings & 2...
Replies
4
Views
1K
We have some shunt-wound DC motors that are used are servos (so operate over a big speed range and in all 4 quadrants, motor and generator both...
Replies
6
Views
2K
Hi there, I got a call to a job, table saw (wood) tripping C/B straight away. 4kW motor on Star Delta Starter. So I get to the job, after some...
Replies
2
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock