Hello All.
Not been on here for a while, hoping you guys can help me with this one.
We installed 185mm single copper core aluminium armoureds (2*185mm per line conductor each run 170m) to an MCC feeder. The intend was to use the aluminium armourings as the main CPC.
My question is, how can i work out the CSA of the armouring for the CPC?:confused::confused:

Thanks in advance
 
There can be issues when using single core cables. Namely circulating currents between sheaths of the cables and eddy currents being generated where they pass through a steel glandplate or enclosure.

See regs 521.5.2 and 523.10
 
Thanks bomjac, I have installed non-ferrus glandplates in both MCC`s, the customer did suggest a wooden plate...... was a good chuckle for 5mins.
 

Reply to Parallel feeder cable Question in the Canada area at ElectriciansForums.net

Similar Threads

Did an EICR that passed 5 years ago Several things in the picture raised concerns for me. Comments please - photo at end First photo shows a...
Replies
9
Views
1K
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Replies
2
Views
1K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
Hello, With regards to Trimble software for bs7671 cable sizing. I understand that a three phase circuit (No neutral) is one circuit and this can...
Replies
7
Views
3K
Hi All, I’m after some advice. I’ll cut to the chase but I can give more detail if needed. A 400A sub main supply needs to be ran 100m, a pretty...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock