Discuss PAT On A Hand Dryer in the Electrical Appliances Forum area at ElectriciansForums.net

R

russty

Anybodys thoughts on this hand dryer ive come across?
Came across the hand dryer doing some PAT in some offices. The hand dryer has been put onto a plugtop in a toilet, which i know should really be into a fused spur. Thing is its connected to a RCD socket above which is on its own dedicated circuit back at the board and is in a zone 3.
Do i pass it and give a advice note that its should be terminated into a fused spur or simply just fail it?





15062011389.jpg
 
It's unconventional - do the manufacturer specify it should be hardwired?
I'd consider the implications - it's in an office rather than a pub, but what else is likely to be plugged in there? Is anyone going to have to plug it in with wet hands?
I'd probably go with what you suggested - test it as normal and recommend the socket is replaced for a FCU.
 
Looked at it logicaly and with the hight of the socket couldnt emagine it being touched fairly often. Give the recomendation and up to the client to decide what to do.
 
Two thoughts whats the power rating of the unit ..can it be safely used on a 13a plug for continued use? If so is the plug top a high quality one or a 99p shop special ?



the fact that it is on a plug means its easier to pat test otherwise you start to need breakout boxes etc or start using mft's etc.

Are you providing fixed testing at the same time as the Pat ?
 

Reply to PAT On A Hand Dryer in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hi guys I am wiring Some toilets in an office building and I have the dyson airblade where the cable comes back of the unit. Is it acceptable...
Replies
1
Views
2K
Hi, I perform annual PAT checks for my company (office and workshop). The Apollo 400 machine we use has recently gone for calibration and service...
Replies
7
Views
922
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
A recent EICR turned up a fault: an RCD fused spur was feeding a socket and a shower pump, and neither socket or pump had continuity on the CPC...
Replies
17
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock