If you are testing the lead separately then 0.10 ohm is not relevant (this is the limit for the connected appliance). Your earth bond reading is relevant to the cord csa and it's length.
 
If you are testing the lead separately then 0.10 ohm is not relevant (this is the limit for the connected appliance). Your earth bond reading is relevant to the cord csa and it's length.

Thanks for the reply

Ok yea it makes sense but wouldn't you allow some resistance for the resistance of the 13A plug and socket contacts? Especially as they can be quite flimsy being just 2 blades pushing on the earth prong.
 

Reply to Pat testing IEC leads in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi, I perform annual PAT checks for my company (office and workshop). The Apollo 400 machine we use has recently gone for calibration and service...
Replies
7
Views
883
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
674
Hi guys and gals, I have a question about the leads to computers (commonly known as kettle leads). I am new to PAT testing so please bear with...
Replies
0
Views
954
Hi, I carry out PAT testing on landlord appliances for letting agents in rented accommodation. Occasionally some of the items I cannot access...
Replies
5
Views
729
Hi. The question is..... can saturated ground affect earth resistivity testing equipment? Some days there's an unacceptable earth reading, another...
Replies
8
Views
358

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock