Posting a message to the forum will remove the above advertisement

Discuss PAT testing of Handwash units Yes or No in the PAT Testing Forum area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. LTS_SPARK
    Offline

    LTS_SPARK EF Member

    Having a few thoughts on what should and shouldn't come under PAT testing under the COP 4th Edition.

    I have no doubt wall heaters screwed to the wall and connected via a flex and FCU should be PAT tested, along with hand dryers, but does the same apply to Handwash units and 5-10litre water heaters which are plumbed in to the water supply on fixed copper pipes, but also connected via a flex and FCU ??

    Just want to get the facts straight before I approach the customer.

    Long standing Sparky but new to PAT testing.
     
  2. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Appliance - computer says yes please :)
     
  3. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Yes of course they should be tested
     
  4. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    yes it should be tested I've always done it under EICR not doing a lot of pat testing out of interest how do you do a PAT test for such items
     
  5. bigspark17
    Offline

    bigspark17 Electrician's Arms

    Location:
    wales
    Yes definatly should be tested.. use a mft.!
     
  6. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    but this is not PAT testing is it my question was more if I was sent to with a pat tester how do you pat test this type of equipment
     
  7. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Ant it's In Service Inspection and Testing of Electrical Equipment, the COP for ISITEE doesn't say how to test it just that it has to be tested, PATesting is old hat now, neither can you test as part of an EICR as strictly speaking it's not part of the fixed wiring. To add if I was quoting a price for someone who wanted their equipment tested, to to put it another "can you give me a price for PATesting my appliances" I would price items such as your example at a different rate, but then most customers wouldn't realise the difference, because most are unaware, or don't understand what is required. Sorry for the lecture.:rolleyes::) This why I feel the " you only need to competent to What was PATesting" needs, in my opinion, revisiting and upgrading.
     
    Last edited: Mar 19, 2017
  8. LeeH
    Offline

    LeeH Insert witty monkey comment here. Electrician's Arms

    Location:
    Lincs
    A 'PAT tester' may not have the skills required.

    Any spark has and would use a MFT or a traditional tester with a bastardised lead.

    The point is they must be done, the code of practice is not just for appliances with plug tops.

    EDIT, beat by Pete.
     
    • Like Like x 1
  9. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    Thanks for the info
     
  10. LTS_SPARK
    Offline

    LTS_SPARK EF Member

    Thanks for the replies and thoughts. Was just a little unsure as they're plumbed in so not so easy to move.
     
  11. LeeH
    Offline

    LeeH Insert witty monkey comment here. Electrician's Arms

    Location:
    Lincs
    Safe isolation, remove from fcu, test.
     
    • Like Like x 1
Loading...
Similar Threads - testing Handwash units Forum Date
Silly question GS38 probes and dead testing Electrical Forum Yesterday at 7:34 PM
Metrel insulation testing issue Electrical Forum Thursday at 3:05 AM

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job