Discuss PAT testing prices and companies in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reply to PAT testing prices and companies in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi, I perform annual PAT checks for my company (office and workshop). The Apollo 400 machine we use has recently gone for calibration and service...
Replies
7
Views
885
Hi all, Not sure if asking about rates is allowed, but I'm wondering what people's thoughts are on chargeable rates for PAT testing. Baring in...
Replies
5
Views
765
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
676
Hi, I carry out PAT testing on landlord appliances for letting agents in rented accommodation. Occasionally some of the items I cannot access...
Replies
5
Views
734
Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
467

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock