Discuss PE from metal back box to socket in the UK Electrical Forum area at ElectriciansForums.net

I don't do it on plastic I started in 2006 so guess we were on 16th and no longer a requirement then. I know from doing periodics thinking back the one fixed lug making contact with the brass ring round the screw hole was deemed sufficient, was brought up on site work so wouldn't often do more than required in that situation and old habits die hard whichever side you fall.
 
Not required. Back box is earthed by face plate screws. Could be argued you shouldn't be working live hence you shouldnt be opening it without killing power anyway
 
It’s niether extraneous or exposed
May sound bizarre on first reading, but the metal backboxes is indeed an exposed conductive part.
This is because it is not insulating and may become live under fault conditions.
The touchable criteria could be indirectly, for example installed into a metal framed wall with a shelf fixed on the other side. Regardless, There is no requirement for any specific standard of insulation to the wall that encloses the back box and the back box is the only thing under the control of the electrical installation.

Having said all that, the screw is deemed enough to earth it!
 
Agreed on both point. But A) why have the termination screw o the box if it's not mandatory and B) why was I told to do it and have always done it since I was a lad?
Somewhere to hang your cpcs if the wiring is Twin and cpc, on a lighting switch maybe, where there is no earth connection on the switch?
 
Seems just like a nice finishing touch, takes less than a minute, and on surface-mounted metal-clad stuff in a workshop with multiple users of varying skills it makes sense as an extra safety element, imho
 
Also helps to use up that roll of 1.5mm green/yellow 6491 that will not ever end.
As with @Murdoch - any upgrades to metal switch faceplates is a must.
 
Also helps to use up that roll of 1.5mm green/yellow 6491 that will not ever end.
As with @Murdoch - any upgrades to metal switch faceplates is a must.
The termination block is there for when a switch is to be fitted, stops a floating earth
You bin watching Sy Fy movies Mate floating earth WTFs that all about.
 
Apologies for the late arrival to the conversation,

So, does anyone know where in the regulations (BS7671) it says, you can use the lug hole of the metal box as an earthing point?

I think the regulation 411.3.1.1 applies, As does 132.1

The only question is. Are the metal back boxes classed as an exposed conductive part when buried in the wall?????.... I would agree when it’s fitted into the wall it may not be an exposed conductive part, but again if it’s not stated within the regulations, it’s all about interpretation.

Then again, it’s all about the idiots who live in the house, if they take of the socket of the wall then the back box is an exposed conductive part. Agree they would deserve an electric shock for being stupid in doing it live, (but these are the same people who put 30 amp fuse wiring into a 5 amp fuse carrier because the 5 amp kept blowing) … therefore its incumbent on the designer to take into account the layman and woman who will be living in the installation afterwards. hence 132.1

I don’t know if I agree its not good practice to earth the metal box. I think it is, and makes a statement about the standards the electrician is aiming for.

but I am on the fence now about it being a bad practice in not doing it… possibly it’s just lazy….

OK Tin Hat on …..

And

Merry Christmas and happy new Year to everyone.
 
Just as an addition/clarification GN8 Amd3 states at 9.7
'For flush metal back boxes with one fixed lug and one adjustable accessory fixing lug, as shown in figure 9.8, it is always desirable to provide and earthing tail.'
 
The only question is. Are the metal back boxes classed as an exposed conductive part when buried in the wall?????.... I would agree when it’s fitted into the wall it may not be an exposed conductive part, but again if it’s not stated within the regulations, it’s all about interpretation.
The metal screws holding the switch to the back box would be an exposed conductive part though , so I would say that a metal box would have to be earthed even if the accessory did not need an earth, unless of course they where nylon screws.
 
The metal screws holding the switch to the back box would be an exposed conductive part though , so I would say that a metal box would have to be earthed even if the accessory did not need an earth, unless of course they where nylon screws.

Indeed, but if you look at the construction of a BS1363 socket outlet, the screws become Earthed when fully tightened up, and thereby, Earthing the backbox via 1 or 2 of the fixed lugs.
 
Indeed, but if you look at the construction of a BS1363 socket outlet, the screws become Earthed when fully tightened up, and thereby, Earthing the backbox via 1 or 2 of the fixed lugs.

Yes I know That's why I said an accessories that does not need an earth for example a plastic lights switch :)
 
I have found on sockets (on several occasions) on an RFC, where the two incoming earths are terminated in the metal back box. And the installer has relied upon the screws to earth the socket, with no strap fitted!

Measuring a somewhat higher than expected Zs at the socket, and giving the screws a quick tighten (when Zs drops) usually gives the game away.
 
I have found on sockets (on several occasions) on an RFC, where the two incoming earths are terminated in the metal back box. And the installer has relied upon the screws to earth the socket, with no strap fitted!

Measuring a somewhat higher than expected Zs at the socket, and giving the screws a quick tighten (when Zs drops) usually gives the game away.

I’ve honestly never seen this done?
 
Over 50mm2 to be classed as exposed conductive part
Maybe truet, but in terms of IP ratings that's not good. To be effectively class II it would need double or reinforced insulation, neither of which a socket has.
Wagobox or even surface mount back box yes, but metal socket box even though it's not an appliance i would still treat the back box as the enclosure as the wall is not part of the electrical installation.
 

Reply to PE from metal back box to socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
906
Hey, I lifted a few sockets from a wall so I could paint without having to cut in around them. I haven’t lifted any light switches yet. When...
Replies
4
Views
940
I didn't get a picture so will have to wait until I go back again but I've done a crude drawing of what was there. Its in a commercial set up...
Replies
13
Views
2K
Hi all, I am an experienced DIY electrician and I just wanted to ask a quick question about something since I am new to this forum, if it hasn’t...
Replies
11
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
865

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock