Discuss Pendant backbox - what's going on? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
137
Can anyone please shed some light on what this is/what is going on here?

This old apartment is wired in conduit, which is also the earth provision. In the bathroom, this metal 'thing' is screwed into the side of the pendant backbox. Out comes a fly-lead also connected to the pendant backbox, and in goes a neutral from the light, as does another leading off in another direction.

If I disconnect the neutrals and stick them into a wago the light fails to work. I found it just as the day was wrapping up, so I haven't fully investigated, but I'm assuming they're using the conduit to provide a neutral? If so, then why is the RCD not tripping and what is this odd contraption?



Screenshot 2023-03-01 at 18.18.37.png
 
Ahhh ffs, I think you are right. Well, this job is about to get interesting. The reason the light came down in the first place is because the LED was flickering whilst the switch was off, suggesting some leakage going on. Now I've got this in the mix.
 
That is almost certainly an MI cable pot. I'm not clear as to what you are trying to explain.
 
That MI seal is poking into the BESA box instead of being seated inside the gland screwed into its conduit entry. Advantage; you can see and get to the seal, offset against it hogging the space inside the box. The MI sheath is the earth but shouldn't be serving as the neutral; that practice was used historically (earthed concentric wiring) but not in domestic work. If someone has picked it up as a neutral he's a very naughty boy.

There should be two or three sleeved conductors exiting the black disc in the end of the pot. Some later seals also have an earth tail spot welded onto the pot itself which is securely in contact with the MI sheath, but more commonly the earth connects only via the gland (which you can't see) and box as a conduit would. Try to avoid flexing the conductors too close to where they exit the pot because if they break off, or the disc comes loose, you have a more complex job on your hands.

A failed or damaged seal allows the MI insulation to absorb moisture from the air and its insulation falls. If one end or the other has got very bad or there's a puncture in the cable sheath somewhere, it might have fallen low enough on a switch cable to cause flashes when off. Although, if the MI doesn't contain both the PL and SL conductors, that's not the problem here. If it's suspect, disconnect all cores and megger to the sheath.
 

Reply to Pendant backbox - what's going on? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, Got an antique light fitting that for some reason she wants putting up (can't say I love it haha) however it didn't come with any...
Replies
9
Views
3K
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
922
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock