Hi all.

Just a question which seems to get me a bit confused about PFC testing. I understand that the value of PFC you put on a EIC or any other form is the highest value of either the PSCC or the PEFC. Now when you get the reading on your meter (which is sometimes displayed with the Zs value) which one is this? Has the meter automatically worked out the highest value between the two or only given you one? When you plug in the 13 amp adapter into the wall to test Zs is the PFC reading the highest of both the PSCC and PEFC? I understand that all meters operate differently, however how are you able to differentiate between the two tests ?

Thanks for reading and I hope you can help me out !!!!
 
I may have missed something, but your PFC etc will be in amps and the Zs or impedance will be in ohms. The Megger tester I use has a different function for both. I'm assuming whatever you use combines both values. For PFC and depending on the earthing system i test line/ earth and line/ neutral recording the highest value as PFC.
 
As far as I'm aware it is taking both readings and displaying the highest, it does with Martindale testers anyway.

jjnr78 a lot of the MFTs now when doing the Zs live test will give you the main display of the earth fault loop impedance in ohms and in the bottom r/h corner will be a smaller read out of the PSCC in amps normally, not Ka
 
Last edited:
Thanks for your replays. Would have thought they would display the two different values for PSCC and PEFC? I suppose only way to find out would be to read the manual for whatever meter you were using! Thank you both for your help.
 
PEFC, is calculated using the voltage and the impedance (Z1 + Z2) of the Line and CPC.
PSCC, is calculated using the voltage and the impedance (Z1 + Zn) of the Line and Neutral.
Unless your tester conducts both tests at the same time, or has a funtion where it will remember the value for one test, when you conduct the next, you will have to remember the value yourself, and compare it against the value for the second test conducted.
 
Last edited by a moderator:
So to measure the PFC at the origin of the supply, this would consist of the two tests you've mentioned above? I can understand with a two lead tester but what about a three lead test machine?
 
So to measure the PFC at the origin of the supply, this would consist of the two tests you've mentioned above? I can understand with a two lead tester but what about a three lead test machine?
My tester (Metrel 3000i) uses 3 leads, but different positions on the selector.
I conduct the PSCC test, switch the selector, conduct the PEFC test, record the highest value, then disconnect the earth conductor and conduct the Ze test.
My tester may well have the facility to remember the two values, and even display the highest.
I haven't noticed it, or bothered looking for the function, as remembering the value for the time between tests is not something I have a problem with.
You ever hear someone muttering to themselves 0.39, 0.39, 0.39....., that's probably me conducting the tests.
 
I use a Fluke 1651 with 3 leads, when using this tester you need to connect all the leads to carry out a Ze P-E on Loop setting, the value displayed at the bottom is the PEFC. You then need to change the setting to P-N still on Loop to measure the PSCC. The highest reading is your PFC. So it seems the answer to your question is, it depends on your tester.
 
you are talking about 3 different checks I feel here.
1=Ze ie earth loop impedance, 3 lead if sep earth, 2 lead if pme.
2=PEFC ie 2 lead line + neutral
3=PSCC ie 2 lead line+neutral
 
My tester (Metrel 3000i) uses 3 leads, but different positions on the selector.
I conduct the PSCC test, switch the selector, conduct the PEFC test, record the highest value, then disconnect the earth conductor and conduct the Ze test.
My tester may well have the facility to remember the two values, and even display the highest.
I haven't noticed it, or bothered looking for the function, as remembering the value for the time between tests is not something I have a problem with.
You ever hear someone muttering to themselves 0.39, 0.39, 0.39....., that's probably me conducting the tests.

Thanks Spinlondon. This makes it clear for me as I find Metrel manual very confusing on this part of testing!
 

Reply to PFC Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Just thinking about selling MFT's and single test equipment. The idea being I buy stuff from Ebay and sell it on ebay, which I am doing at the...
Replies
0
Views
290
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock