Noods

Hi All

purchased an old cincinatti ( USA built) workshop phase 3 pillar drill.. Needed tlc.. Unfortunatly the previous owners had removed the connection plug.. Drill delivered to me unseen..

In the junction box I have 3 red wires going into 3 blacks and one green wire into a green and yellow..

At at the plug end I have 3 blacks and the green and yellow..

As as a car tech I'm a bit confused..

Many thanks..
 

Attachments

  • image.jpg
    231.4 KB · Views: 13
It looks like a 3-phase machine without a neutral but you should find the info plate and confirm this first before connecting. Was the machine already running in the UK before you bought it? If it was purchased from the US the voltages and supply frequency won't be compatible with your supply.

The green/green-yellow will be the earth, the 3 blacks/reds will be the 3 phases. This thing is probably rotation critical so if you connect it up and it runs in reverse you'll need to swap over any two of the 3 phase connections.

Please bear in mind you're dealing with a 400v supply so if you're unsure how to prove the circuit is isolated or you're not comfortable with your abilities rather get a sparky to assist you.
 

Reply to Phase 3 wiring colours? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
Looking for advice for the following: Bosch Induction cooktop model NIT8669SUC ) came with 3 bare wires (Black, Red, Green) but my wall has a 4...
Replies
0
Views
725
Hi, I Bought a 32A EV Charger, it comes with a CEE wall plug. I need to use it with a 60A range recepticle which I use to plug in my welder. So...
Replies
3
Views
1K
I built a prototype Dog Dryer. Took a dryer element and pushed it into a vent pipe. Cut out vent pipe to access the two spade connectors on the...
Replies
0
Views
1K
New one for me... Commercial building (museum), 3 phase board 16A MCB, 3 x 2.5mm singles run in 20mm conduit, ending up at an FCU. All fine. The...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock