Can you trace the tails between the meter and the incoming side of the isolator.
yes right next to it, why?
[automerge]1588271646[/automerge]
Understand the inconvenience of the down time, however the phase rotation can be reversed at the meter, L2L2 L3L3 swapped as complete pairs. No reversing is needed on the installation side.
hi dave , I am not sure i follow what you mean here. surely if anything is reversed upstream (so to speak) the end appliances that rely on phase rotations for their direction (3 phases motors in this case) will be running in the opposite direction . Unless i am missing something obvious .
 
Last edited:
yes right next to it, why?
[automerge]1588271646[/automerge]

hi dave , I am not sure i follow what you mean here. surely if anything is reversed upstream (so to speak) the end appliances that rely on phase rotations for their direction (3 phases motors in this case) will be running in the opposite direction . Unless i am missing something obvious .
I cant explain the science, Marconi a member on here (the professor) is the man.
So im not even going to attempt.
 
yes right next to it, why?

Because as I already said the meter is usually installed with standard rotation otherwise it is not within its certification. You are saying the rotation at the isolator is wrong. If the tails are straight then it is a DNO issue, if the tails are crossed then it is a customers issue. Albeit that they would need to pay the DNO to swap them.
Having non standard rotation in an installation is not a panic situation as long as every one electrical is aware of it.
 
thanks dave ,I will do but the only potential problem that I see with that is that the customer will inccur more down time for his premises and the rotation of all the 3 phases motor will need to be reversed .

Have you checked the phase sequence? Is it consistent throughout the installation?

If all the motors are running the right way then either they have all had rotation corrected, it has been corrected elsewhere or there is a mistake in your testing
[automerge]1588273554[/automerge]
Understand the inconvenience of the down time, however the phase rotation can be reversed at the meter, L2L2 L3L3 swapped as complete pairs. No reversing is needed on the installation side.

That won't change the phase rotation problem that the OP thinks they have. It will only change the rotation at the meter.
 

Reply to phase rotation incorrect at origin of install . in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
681
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Help please, this is my first post on this subject regarding solar panel / battery installation into house with 3 phase supply. I am a DIY level...
Replies
0
Views
1K
I was looking at an image in another post - copied below - and noticed the label 'Rotation anti-clockwise' on the lower MEM item of switchgear...
Replies
2
Views
2K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
590

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock