Discuss PIR codes, help please in the Australia area at ElectriciansForums.net

S

sjm

Hi guys.
Just wanted to ask what code you would give an old wylex fuse board with wooden enclosure. It does have the plastic (plexolin I think it's called) plate at the back.
Also 2.5 T+E with 1.0mm CPC used for a ring main on a 3036 fuse.

Thanks in advance.
Steve
 
code 2 for the board. code 4 for the 1.0mm cpc IMO.
 
Hi mate, 2.5mm with 1.0 earth is fine as long as all test results are o.k.
Wooden back wylex board - not sure, as long as all loads are not over 60A with diversity then they are o.K from a PSCC point of view as the DNO fuse covers this with its 16.5KA rating. They comlied when they were installed, It has been modified with a paxolin back, hmm difficult. I think they don't comply now due to ignitability, which is somewere in that red book. I would possibly code 2 if there was signs of damage and burning, or in your case I would probably code 4 - complies to previous edition.

oh p.s. its Paxolin ;-)
 
just like millionaire. ask the audience, yes that's what i thought . only joking steve!
 
Well I'll have my 10p now then.

IMO a 2.5/1.0 ring final on a BS 3036 fuse is a code 2 as it fails the adiabatic equation for this type of fuse.

The board itself I'd have no problems with, the lack of RCD protection possibly, depending on circumstances.
 
IMO a 2.5/1.0 ring final on a BS 3036 fuse is a code 2 as it fails the adiabatic equation for this type of fuse.


could this not depend on the length of the ring, and comply if the ring was short enough for the 1.omm cpc to be adequate?
 
You are indeed right lenny adiabiatic comes out at 1.15 I think, however someone on our lot phoned the IET about it a couple of years ago as a result of an argument like this and was told that it was OK if it met the rwquired results, in their opinion...

Suppose its all down to interpretation again.
 
Well I'll have my 10p now then.

IMO a 2.5/1.0 ring final on a BS 3036 fuse is a code 2 as it fails the adiabatic equation for this type of fuse.

The board itself I'd have no problems with, the lack of RCD protection possibly, depending on circumstances.

What value for k are you using?
 
TBH there are so many different factors that could influence the outcome it's difficult to stamp an assured answer one way or t'other.

I calculate to 1.15 (spot on somerset :cool:) ergo a 1.0mm cpc is insufficient to withstand the fault current for the given time.

All IMO.:)
 
If its missing its spark cover then its a code 1 code 2 if its in place[/QUOT

and what's the code for 2" nails in the fuse holders. minus???

nothing wrong with a nail in the fuse holder eliminates neusance tripping code 1 i think , i hate rewireable fuses they should be banned so easy for mis use and electric shock every time you take the fuse carrier out you expose live busbars , yes i know the should switch it off when the do it but its the general public we are talking about and 80% just pull out the fuse its a miricle people havent been killed with them or perhaps they have
 
looks like your'e returning to your normal self, nick.
 
TBH there are so many different factors that could influence the outcome it's difficult to stamp an assured answer one way or t'other.

I calculate to 1.15 (spot on somerset :cool:) ergo a 1.0mm cpc is insufficient to withstand the fault current for the given time.

All IMO.:)

Is 115 for k an appropriate value to use, considering the conductor is unlikely to initially be at 70ºC or greater?
 

Reply to PIR codes, help please in the Australia area at ElectriciansForums.net

Similar Threads

Hi Help please with the adiabatic I am doing a small design for my course and I can't figure it out. Any advice will be appreciated. Ring Final...
Replies
15
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello, I’m in dire need of help. here is the question A kitchen Ring final circuit is wired in 2.5/1.5mm T&E and protected by a 32A type B...
Replies
7
Views
975

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock