Many thanks for your codes list ,very helpful.is there a book i can buy to assist further on this matter.cheers tc
Discuss PIR codes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
One small point to add, its not satisfactory to have one or two RCD's to BS 61008 protecting more than one circuit. each circuit, as described in previous post by spinlondon, should be protected by an RCBO to BS 61009
Why not?One small point to add, its not satisfactory to have one or two RCD's to BS 61008 protecting more than one circuit. each circuit, as described in previous post by spinlondon, should be protected by an RCBO to BS 61009
tc50 guidance note 3 also have a look at the little book by the esc best practice guides : Electrical safety council the one you want is the best practice guide 4 which gives you the new coding for pir's
Nickblake there is no such thing as a 17th edition consumer unit, its how you configure the board that will determine whether or not your installation complies. i will agree with you that not every circuit needs RCD protection.
If you look at the list supplied earlier you will see where RCBO's are indicated. any other circuit must be individually assessed. the garage shed that you mentioned, being outside the equipotential zone is a case in point and needs RCD protection
For cascaded RCD's the upstream RCD could be a time delayed or Type S with an ordinary RCD after that. in the case of your shed the TDR could supply the cable to the shed (to protect the cable) and an RCBO to protect the tub circuit etc. this will provide discrimination between the two RCD devices and give the best protection.
Reply to PIR codes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net