On A PIR today on some offices that have been cleared out and the building ready to sell..

There is a suspended ceiling across the whole of the ground floor and up the stairs, In the ceiling tiles there are many GU10 downlights that are Fire rated.. around the fitting on the tiles it has gone slightly brown where the lamp has got hot..

Also the circuit is wired in 1.0mm T&E and there is 17 fittings on a B10 amp MCB.

What recommendations or code would you put on this..?
 
hmmm for the 1mm cable whats wrong with that ??

as for the lights scorching the tiles its probably just bad selection of equiptment etc... how many times you taked a batten holder to find the plastics totally goosed due to heat!!
possibly a 3 for the scorching unless there were signs of obvious fire risks!!
 
17x 50 watt ?
850 watt
Refeence method 101 = 10.5 amp The worst case is surrounded with insulation in a stud wall at 8 amp
so it seems current carrying capacity of the cable is dependant on the reference method you have for the circuit and also length of circuit for volt drop

I suspect the tiles have a fire rating and are unlikely to burst into flame,but transfering the downlighter heat to the point of evidence of marking of the tiles needs caution

If the volt drop is ok I dont see a coding being required,but perhaps a recomendation that a metal plate or such, be used to minimise the heat transfered to the tiles
 
So maybe just a note to say i recommend that low energy lamps be fitted to reduce the amount of heat caused by the GU10 lamp further reducing fire risks?
 
cant see you need to rec energy lamps, most likely rec 35 wat lamps instead of 5o w which is probably what they should be anyway
 

Reply to PIR... GU10 Downlights in suspended ceiling?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
927
Hi, I have just bought a house which has a downlighting system in the kitchen. I want to replace the bulbs with Philips hue smart bulbs (GU10)...
Replies
2
Views
2K
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K
Today i purchased an Ansell PIR motion sensor light to replace my old one. The wiring outside consists of blue, brown and yellow (with dashes of...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top