Discuss PIR sensor wiring for Stairs in the UK Electrical Forum area at ElectriciansForums.net

Midwest

-
Esteemed
Arms
Reaction score
10,616
Silly question time. I've never wired up PIR sensors for stairs before.

Today I went to replace a 'faulty' sensor, on the grd floor of stairs. Tested sensor, which had 3c to it, but think the installer had connected the wires incorrectly; sw/L (black sleeved brown) was in the L terminal & L (brown) in light on or sw/L terminal. Had 240V in L terminal, nil in sw/L terminal. Then resident popped out of flat on 1st floor and set off 1st floor PIR. I then had 240V on both L & sw/L terminal, 20mins later I gave waiting for 1st floor PIR to time off.

My silly question, is the PIR's sw/L would be just linked together, hence 240V at my faulty PIR, until the other PIR timed out?
 
Some electricians use black sleeved brown as the permanent live on this sort of thing along with emergency lights, whereas most use the brown. Nothing wrong with either way, we just need to be aware.
 
Thanks for the advice chaps. The set up is quite large, probably hundreds of these things. Got the details of the PIR, and phoned the manufacturer. The settings are altered by an IR remote, which we haven't got one of. So thats the next thing to get.

Just wanted some guidance on the wiring, just to make sure, as it were.
 
lost my rag with one of these once, it also had an EM and test circuit.

Apparently it had never worked properly since installation.

Spent ages working it all out then lost track of what was what.

Ended ripping it all out and rewiring, luckily it was all surface mounted an fed from click plugs.

you live and learn.......
 
Midwest. Do you have an electric centre wholesaler near you. They have just started selling remote emergency lighting stuff. Prices are really cheap.
May be worth checking them out to see if there compatible with your system.
 

Reply to PIR sensor wiring for Stairs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
534
I wonder if any helpful electrician could throw some 'light' on this question I have regarding changing the switching configuration of my current...
Replies
1
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello, DIYer and first time poster here. Recently bought a house built in 1925, and am gradually working through adding and replacing the wiring...
Replies
9
Views
2K
Hi all, I have some outdoor lights, and I want to update the circuit to add a bit more functionality. I have drawn a little picture of what I...
Replies
15
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock