- Reaction score
- 25,531
SWA supply to garage may need RCD protection, we don't have enough information.
Discuss Planning garage sub-main project in the UK Electrical Forum area at ElectriciansForums.net
Although it might not need to be 30mASWA supply to garage may need RCD protection, we don't have enough information.
Well I was thinking twin and earth (e.g. 6mm) would be cheaper and easier to run under floor boards etc.Skip the twin and earth in conduit and run swa straight to board. What is the purpose of the t+e? Looks like part of that board isn’t rcd protected, get an mcb to fit it
Reply to Planning garage sub-main project in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.