Discuss Please identify this isolator in the UK Electrical Forum area at ElectriciansForums.net

ChrisElectrical88

-
Mentor
Esteemed
Arms
Reaction score
1,650
Come to carry out some works on this property. This isolator is between the DNO Head and Meter.

Full set up picture also included. Old TT System now convered to PME.

Cheers

IMG-20190902-WA0003.jpg


IMG_20190902_130721.jpg
 
The TEST button certainly doesnt work. Its also rated at 63A and when the DNO have changed the head its now a 80A Fuse.

The install was TT up until 3 years ago. Now its PME.

Its on the DNO side of the meter, do you think its worth getting them to come and remove it?
 
There are many VOELCBs being used as DP Isolators.

If the supplier thought that the old VOELCB was capable of carrying the new loading then they would have left it in place. A bit odd to leave it between the meter and the intake though.

If you have any doubts have a good old sniff around the switch and if it stinks of fish then it may have too much load passing through it.
 
. @OP please,please,please open the box.
 

Reply to Please identify this isolator in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
858
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
630

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock