Discuss pond heater 2kw in the UK Electrical Forum area at ElectriciansForums.net

C

conradj100

Hi I'm new to this forum.

My dads fish pond has a 2kw heater and recently wasn't working. When investigating into the problem I put it down to a faulty heater as when plugged in it trips the inline RCD. When the load switch line to the heater is not connected the rcd plug does not trip and there is 230v at the supply side. As soon as the load sw line touched the terminal it trips. This is how i worked out it was faulty.

However he purchased a new heater and that was faulty water dripping out the power on light.
We decided to plug the old heater into a separate circuit and filled it up with fresh tap water. This worked, didn't trip the rcd and heated up.

So we re-plumb the old heater back to the pond system and trips instantly.
I kept trying and for some reason the heater stayed on after few try's. I then plug pumps in one by one and found one pump causing the heater to trip.
I changed this pump for a new one thinking this was the problem but it still trips.
I have even run it off a different circuit and it still trips the rcd inline plug.
It trips when nothing is connected which makes me think its faulty but did it work with fresh tap water?

Anyone got any ideas on how to get this to work.

Thanks
 
The heater is faulty (heaters can be funny things as they expand and contract as they heat)
Water and electric do not mix I recommend you get an electrician to look at this.
 
also, the RCD has tripped so many times itmay be knackered.
 
also, the RCD has tripped so many times it may be knackered.
 
Replace the heating element !
They can develope pin holes and leaks
Sometimes these will come and go for a while
but the cure is to replace the element
faults don't fix them selves
 
Thanks he has ordered a new heater. I just thought it was strange that it worked with fresh tap water and not when plumbed into the pond system.
 

Reply to pond heater 2kw in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
595
I have a fairly recently installed consumer unit with an RCD, between it and the garden there is another, much older (25yrs?) RCB (big Wylex...
Replies
11
Views
2K
Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
788
I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock