Discuss Possible failed RCD in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
5
Hi,

I would have thought it unusual for an RCD to fail? However, I have come across a Wylex WRS80/2 which gives >400ms reading for the 1X RCD test using a Megger 1552MFT. A no trip fail.

Could there be some other reason for this result?

Any help appreciated.

Regards,
Trenelly
 
It's protecting various circuits. My test was at a socket outlet.

The problem is usually a load with a capacitor still connected, such as a fridge or fluorescent light. The capacitor holds a charge for a period after power is disconnected and fools the meter into continuing to record voltage after the RCD has disconnected the supply.
As above, test the RCD with all loads disconnected.
 

Reply to Possible failed RCD in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
349
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
625
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi all, Great forum with lots of advice read and greatly received over the years! I have a question here that I am hopeful somebody here can...
Replies
16
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock