6
Doing up a bungalow 3-4 days a week, currently half finished!
When we leave we switch off sockets and shut off water. Sometimes when switching off the socket feeding tv or the socket feeding the recliner transformer (luxury!) the RCD trips (not the MCB for the ring).
The sockets are newly installed BG Nexus metal white with chrome switch.
Searching on line there were tripping issues with this series around 2010, when switching off when under load, but mine are not old stock!
If you jab the switch it hardly ever trips but if you switch it off ‘normally’ it trips about 50% of the time.
What could possibly be wrong with a reasonable quality socket outlet or could it be a wiring issue?
 
Hi - perhaps confirm polarity is correct at the outlet? I'd like to think they dis the L before N in DP outlets, but I've never confirmed it.
 

Reply to Possible problem BG Nexus sockets? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hey, I lifted a few sockets from a wall so I could paint without having to cut in around them. I haven’t lifted any light switches yet. When...
Replies
4
Views
950
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
447

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock