Hi everyone.

I basically wanted to check to see if what I propose is correct.

I had an electrician come round (pre covid) to install power to my garage (Detached from house). This is the setup he used.

  1. Spur off socket on ring main a short distance to a 13A switched FCU
  2. Cable from the FCU through external wall to outside junction box.
  3. From junction box through armoured cable into garage.
  4. Armoured cable into 1x 2G socket.
All works well. The garage was originally powered, but very old so all electrics were stripped out, the only thing left was a 4ft fluorescent light fitting (Cable has been taped up and left dangling), the only powered outlet is the one the electrician has recently installed.

What I want to do is connect the light fitting up (but not stick a plug on it as some people has told me to do).

My plan is to spur off the garage socket to a 5A switched FCU, which will also act as a light switch then connect the existing light to this switch. Does that seem ok?

Also, as the garage is protected by the 13A FCU (inside the house and before the first garage socket) can I have multiple sockets (and the 5A FCU) off this spur?

Thanks in advance.

M
 
TL;DR
I have spurred off house socket to 13A FCU, which goes to garage. My plan is to spur off the socket in the garage to a 5A switched FCU, which will also act as a light switch then connect the existing light to this switch. Does that seem ok?
Theoretically what you suggest is fine. You can add as many sockets as you like but their power consumption is limited by the 13A fuse at the fcu.
 
  • Like
Reactions: DPG
What RCD protection is in place?
 
I would assume it has 30ma as the garage socket has recently been installed.
 
I would assume it has 30ma as the garage socket has recently been installed.

The house circuit (which it is spurred off) is protected by an RCD. Cant tell you if it is 30ma but it says 80A on it. The CU is brand new, installed same time around 4 months ago.
[automerge]1598001716[/automerge]
Theoretically what you suggest is fine. You can add as many sockets as you like but their power consumption is limited by the 13A fuse at the fcu.

There wont be any high powered devices like washing machines. The purpose of the second+ socket it so that I can have power on the other side of the garage. I will only be using one power tool at a time, with the light on obviously! :)
 
Thanks for confirming.
 

Reply to Power to garage sockets and adding light. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
713
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
716
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
419
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock