Would it be practical, or technically possible to economically mass produce 400 volt single phase consumer goods? Light bulbs, kettles, heaters, chargers, TVs, hobs, vacuum cleaners, washers, dryers, microwaves, tools, ect ect?

I'm thinking this would save a lot of copper and make wiring both easier and safer. A 1mm2 cable on a 10 amp breaker would give 4,000 watts of power.
 
Would it be practical, or technically possible to economically mass produce 400 volt single phase consumer goods? Light bulbs, kettles, heaters, chargers, TVs, hobs, vacuum cleaners, washers, dryers, microwaves, tools, ect ect?

I'm thinking this would save a lot of copper and make wiring both easier and safer. A 1mm2 cable on a 10 amp breaker would give 4,000 watts of power.
I'm confused Mate by your conclusions.
 
UK regulation 559.5.1.201 limits lamp holders to 250V.
The biggest cost with cable is usually the installation so reducing the cable size would not save that much. 400V accessories would be bigger and more expensive.
 
It doesn't really matter, different places may settle on different voltages to suit their situation, higher voltages will have issues/costs associated with risk of shock or additional insulation needs etc. Lower voltages with lower shock risk, higher losses and additional costs of conductors etc.

What balance you choose is up to you. In the main internationaly the standard throughout the world is in the 200-250v range - commonly 230v .

This is generally the best balance between all the factors, now it is the main standard most equipment is designed for this voltage, therefore more countries use it, so it's more of a standard, etc.

However there are some countries that are an exception to that in the 110/117v range, these are often purely historical, but once again once in this loop standard voltage - more products - more of a standard etc.
 
UK regulation 559.5.1.201 limits lamp holders to 250V.
The biggest cost with cable is usually the installation so reducing the cable size would not save that much. 400V accessories would be bigger and more expensive.

Can't T&E take 230 volts line to earth? How much does 1mm2 T&E cost vs 2/5mm2 T&E per meter?
 
It doesn't really matter, different places may settle on different voltages to suit their situation, higher voltages will have issues/costs associated with risk of shock or additional insulation needs etc. Lower voltages with lower shock risk, higher losses and additional costs of conductors etc.

What balance you choose is up to you. In the main internationaly the standard throughout the world is in the 200-250v range - commonly 230v .

This is generally the best balance between all the factors, now it is the main standard most equipment is designed for this voltage, therefore more countries use it, so it's more of a standard, etc.

However there are some countries that are an exception to that in the 110/117v range, these are often purely historical, but once again once in this loop standard voltage - more products - more of a standard etc.


Agree. Though would 400 volt as a standard cost more then having 230 volts as a standard?
 
Bizarre idea. And why stop at 400V? Go for 1500V and save even more copper!!


400 volts is already in place, above 1000 volts installations require significantly more complex insulation for guard against partial discharge plus the disconnection times would be difficult if not impossible to achieve.
 
400 volts is already in place, above 1000 volts installations require significantly more complex insulation for guard against partial discharge plus the disconnection times would be difficult if not impossible to achieve.

Why - many large industrial sites use 3.3kV motors and so on.

The voltage isn't fixed at 230 (or 110) - that's just the most suitable for most end users taking into account the factors.

Like why we use 3 phase and not 7 phase and so on - it achieves the best balance given the technology we have
 
Why - many large industrial sites use 3.3kV motors and so on.

The voltage isn't fixed at 230 (or 110) - that's just the most suitable for most end users taking into account the factors.

Like why we use 3 phase and not 7 phase and so on - it achieves the best balance given the technology we have


Right, but 3.3kv with EPR insulation, stress cones and OCPDs to achieve rapid disconnection. The added cost and complexity would outdo any copper savings of using 3.3kv in residential and commercial.

400 volts on the other hand uses PVC insulation and at 230 volts to ground can use standard MCBs.
 
Right, but 3.3kv with EPR insulation, stress cones and OCPDs to achieve rapid disconnection. The added cost and complexity would outdo any copper savings of using 3.3kv in residential and commercial.

400 volts on the other hand uses PVC insulation and at 230 volts to ground can use standard MCBs.

but if you are going to start using phase to phase voltages, then you must start distributing 3 phase supplies - that's a two fold increase in the amount of copper used, plus all switchgear would be three phase etc.

That is a significant increase in costs - a 1.73 reduction in cable size balancing a 2 fold increase in the number of cables
 
but if you are going to start using phase to phase voltages, then you must start distributing 3 phase supplies - that's a two fold increase in the amount of copper used, plus all switchgear would be three phase etc.

That is a significant increase in costs - a 1.73 reduction in cable size balancing a 2 fold increase in the number of cables


No necessarily- you could drop two phases and an earth at each property.

100 x 230 =23,000va / 400 volts= 57.5 amps or 63 amp main fuse.

3 phase would give 33 amps per phase or a 35 amp main fuse.

In both cases the main would use thinner copper, and in the 3 phase example the number of wires do not change in that a 4th neutral is provided as is.
 
No necessarily- you could drop two phases and an earth at each property.

100 x 230 =23,000va / 400 volts= 57.5 amps or 63 amp main fuse.

3 phase would give 33 amps per phase or a 35 amp main fuse.

In both cases the main would use thinner copper, and in the 3 phase example the number of wires do not change in that a 4th neutral is provided as is.

In which case you cannot use 230V equipment!

it's only 400V in relation to a three phase circuit - each breaker is only operating at 230V if you use a single breaker then it must be 400V

All UK domestic equipment is 230v, switches etc

Yes SOME industrial kit is rated at 660V - but even that isn't sufficient, you would need 800v three phase kit for each breaker to open single phase 400V (700V but that's not standard)

A three phase set of breakers does not mean each is capable of opening 400V
 
Why - many large industrial sites use 3.3kV motors and so on.

The voltage isn't fixed at 230 (or 110) - that's just the most suitable for most end users taking into account the factors.

Like why we use 3 phase and not 7 phase and so on - it achieves the best balance given the technology we have
Sorry Julie disagree with your reasoning
 
Your reasoning shows no essence just random wording.

Well I thought it made sense!

It is still possible to use any voltage you want to suit your purpose, yes there are standards such as 230/400, or 380/660, or 1000v as per iec 60038.

However the 230/400 is most common purely because for the most part the current levels are manageable i.e cable sizes, the insulation needs are not onourous and most simple circuit breaker technologies can handle it.

That's why it has become the standard from all the options.

In the same way three phase makes the most sense - its more efficient than single or two phase, but also no less efficient than 4, 5,6,7.... phase.

Does that make it clearer?
[automerge]1600022035[/automerge]
It already exists.

There are lots of equipment that is single phase 400v - but its usually just in industrial settings, for example control transformers are usually phase to phase as there often isn't a neutral.

I took the op to mean why don't we use 400v across the board as standard rather than 230v
 
In which case you cannot use 230V equipment!

it's only 400V in relation to a three phase circuit - each breaker is only operating at 230V if you use a single breaker then it must be 400V

All UK domestic equipment is 230v, switches etc

Yes SOME industrial kit is rated at 660V - but even that isn't sufficient, you would need 800v three phase kit for each breaker to open single phase 400V (700V but that's not standard)

A three phase set of breakers does not mean each is capable of opening 400V

Right.

400 volt rated switches, sockets and light fittings.

Two and 3 pole breakers are already slash rated 230/400Y.
 
Well I thought it made sense!

It is still possible to use any voltage you want to suit your purpose, yes there are standards such as 230/400, or 380/660, or 1000v as per iec 60038.

However the 230/400 is most common purely because for the most part the current levels are manageable i.e cable sizes, the insulation needs are not onourous and most simple circuit breaker technologies can handle it.

That's why it has become the standard from all the options.

In the same way three phase makes the most sense - its more efficient than single or two phase, but also no less efficient than 4, 5,6,7.... phase.

Does that make it clearer?
[automerge]1600022035[/automerge]


There are lots of equipment that is single phase 400v - but its usually just in industrial settings, for example control transformers are usually phase to phase as there often isn't a neutral.

I took the op to mean why don't we use 400v across the board as standard rather than 230v


6 phase is actually more efficent, but I've read that its not worth the extra complexity.

If we were to mass produce 400 volt consumer products, would it be more expensive than 230 volt consumer was my primary questions- though its not really confined to that only. Anything and everything is open to discussion around this subject.


In terms of iec equipment 230/400 refers to 230v ph - e/n and 400v ph-ph

They are only suitable for 400v if they are multiple pole.

True. The only thing that will need to be re-designed are single pole switches.
 
A 400v element is inside it along with 400v controller

We manufacture it for the Scandinavian market

These heaters are these start of something great! Do you have pictures of the internals by chance? What electronic components (rating/type) you use on the circuit board? The tracks on the board? I'm assuming its directly across the mains.
 
6 phase is actually more efficent, but I've read that its not worth the extra complexity.

If we were to mass produce 400 volt consumer products, would it be more expensive than 230 volt consumer was my primary questions- though its not really confined to that only. Anything and everything is open to discussion around this subject.




True. The only thing that will need to be re-designed are single pole switches.

Not really, the whole wiring systems are designed around 230/400v rather than 400v

Switches and breakers are the most obvious, but my whole point is there are and have been other voltages, but the balance of advantages/disadvantages appears to work out around the 230/400v mark which is why it has ended up being the voltage range of choice.

It may be that as technology advances, and we develop new materials, that this balance may actually move to higher, or lower voltages than it currently is, but then do you redevelop everything for a marginal gain.

Where it isn't a marginal gain, then equipment is chosen at different voltages - but such a choice comes at a cost.

I have worked on many sites where all industrial equipment is at 660v, 1000v, 1.5kV or 3.3kV etc in order to reduce the current over large distances, however the cost is limited choice of switchgear, cables etc.

Ultimately its best to have a single standard, which whilst isn't the most efficient in all cases is sufficiently efficient that the advantage of simplicity outweighs the complexity of multiple standards
 
Not really, the whole wiring systems are designed around 230/400v rather than 400v

Switches and breakers are the most obvious, but my whole point is there are and have been other voltages, but the balance of advantages/disadvantages appears to work out around the 230/400v mark which is why it has ended up being the voltage range of choice.

It may be that as technology advances, and we develop new materials, that this balance may actually move to higher, or lower voltages than it currently is, but then do you redevelop everything for a marginal gain.

Where it isn't a marginal gain, then equipment is chosen at different voltages - but such a choice comes at a cost.

I have worked on many sites where all industrial equipment is at 660v, 1000v, 1.5kV or 3.3kV etc in order to reduce the current over large distances, however the cost is limited choice of switchgear, cables etc.

Ultimately its best to have a single standard, which whilst isn't the most efficient in all cases is sufficiently efficient that the advantage of simplicity outweighs the complexity of multiple standards

You're forgetting the history. The world started off with 110-127 volts. Eventually 127/220 in that 110-127 volts was just to low as it could not meet the needs to heaters and motors. Then came the discovery that the advantages associated with 220 volt could be extended to small equipment and associated branch circuits. 220 became the norm- hence why the schuko plug is not polarised.

When 220 volts became the norm for all single phase equipment, people realized that 220/380 met the needs of ever larger motors in typical buildings and long public supplies.

The thing is, today we are stuck on a dual voltage system without any investigation made if 400 volt single phase equipment might be more practical than 230 volt equipment.
 
You're forgetting the history. The world started off with 110-127 volts. Eventually 127/220 in that 110-127 volts was just to low as it could not meet the needs to heaters and motors. Then came the discovery that the advantages associated with 220 volt could be extended to small equipment and associated branch circuits. 220 became the norm- hence why the schuko plug is not polarised.

When 220 volts became the norm for all single phase equipment, people realized that 220/380 met the needs of ever larger motors in typical buildings and long public supplies.

The thing is, today we are stuck on a dual voltage system without any investigation made if 400 volt single phase equipment might be more practical than 230 volt equipment.

No, not forgetting, but the first generation and distribution of electricity was in the uk in the 1880s it distributed ac 250v and 40v for different types of lighting.

I think it was in Godalming

Next was 110v dc in London


I certainly don't think we arrived at ~230v by accident without any thought, in Germany for example they specifically altered all their equipment from 127v to 240v to take advantage of the lower current, without too many issues with high voltage - other countries followed similar changes settling at various voltages mainly in the 200-250v for household and higher for industrial.

The compromise of 230v is fairly recent in those terms
 
No, not forgetting, but the first generation and distribution of electricity was in the uk in the 1880s it distributed ac 250v and 40v for different types of lighting.

I think it was in Godalming

Next was 110v dc in London


I certainly don't think we arrived at ~230v by accident without any thought, in Germany for example they specifically altered all their equipment from 127v to 240v to take advantage of the lower current, without too many issues with high voltage - other countries followed similar changes settling at various voltages mainly in the 200-250v for household and higher for industrial.

The compromise of 230v is fairly recent in those terms


What investigation is there of 400 volts? Remember that incandescent bulbs no longer play a role where high voltages mean higher gas fills and thinner, longer, cooler running filaments. LEDs can be fed via driver. Caps and resistors can drop 400 volts to the required series parellel voltages.
 
The gist of the OP's question is why not make the default single-phase voltage, i.e the lowest voltage available on the system, 400V rather than 230, regardless of the phase arrangement. So discount whether it's Y or delta, single or three phase, and just consider whether 400V light bulbs, hairdryers, phone chargers etc. are sensible and practical and worth the saving in copper.

The answer I suspect is no.

Historically, the choice of voltage was significantly dictated by both carbon-arc and filament lamp design and 120 years ago, both worked better at 120V than 240. Metal filament lamps are stronger, last longer and are more efficient at lower voltages (hence 12V halogens etc.) In the UK, we actually preferred 120V lamps in series pairs for certain stage lighting purposes instead of 240V and projector lamps were 120V fed from a transformer, because 230V lamps were so fragile and inefficient. We got good at making 230V general purpose lamps but 400V was basically unachievable, so there never was a 400V incandescent lighting option. None of that really applies in 2020.

The fragility argument also goes for many wound components, a small 400V transformer primary or relay coil is more expensive to make and more prone to failure than a 230V one, due to having many turns of very fine wire. Even 230V can be a problem - many small mechanical timeswitch motors (e.g. the defrost timer in the freezer and plug-in timers) actually used a 120V or lower voltage motor, fed by a capacitor dropper, because a 230V type would be too expensive and fragile. 400V would be much more of a problem still.

Discharge lamps with ballasts dictate their own voltage and the ballast takes up the difference between that and the supply. So a metal halide lamp running on 400V will take the same current as one on 230V, just at a lower power factor as the (more expensive) ballast has to drop an extra 170V. Only a transformer would solve this.

But, the main event is the switched-mode power supply, where the electronics on the primary side have to operate at the peak voltage of the supply. In most electronic devices, and any appliances containing electronics, the incoming 230V AC is rectified and smoothed to 320V DC, whereas on 400V the DC rail would be 560V. This requires both smoothing capacitors and chopper transistors of a different tier of performance, which certainly with the components available today would significantly impact the price. 560V is definitely at the top end of what electrolytic capacitors are capable of, and at this voltage it is not uncommon to have to use series pairs with balancing resistors. Possible, but probably not economic, given that many such power supplies use so little power that they would not contribute to any realistic saving in copper. Really small loads that use capacitor droppers, like the ballasted discharge lamps, would simply have to use a more expensive capacitor and drop more volts, with no saving in current.

Therefore I think with the state of the art, small power and lighting is still best served in the 120-230V range, with advantages to both voltages but increasingly in favour of 230V now that filament lamps are not a driving factor.
 
Last edited:
Given that the idea of switching to 400V delivered as 2 legs of a 3P system, I'm surprised there's been no discussion about how the change coukd be made. It makes me think of the old joke about the tourist asking a local how to get somewhere - only to be told "I wouldn't srart from here".
With the change, single phase systems would now have two line conductors - so you now need 2 pole protection and switching for everything. So you're no needing a partial rewire of every property. Lights looped at the rose now need altering to take the second line down to the switch & back - physically you may be looping at the rose, but electrically the same as looping at the switch and needing a partial rewire. And of course, you'll need to replace most of your accessories to make everything 2 pole switched. And all your plugs will need replacing for ones with 2 fuses - I remember they had some of those at school for the 110V stuff run from 55-0-55V supplies.
So we've replaced all the CUs, partially rewired, replaced most of our accessories and pkugs and ... we still haven't addressed appliances.
So we also persuade everyone to replace their fully servicable appliances for new ones designed for the higher voltage. And they will be new ones as no supply of second hand ones. The day someone suggests that to me, they will learn some "interesting" vocabulary - unless they are offering to pay for it all.

Of course, there is the alternative of adding a stwp down isolating transformer between the meter and CU - at a cost, and if there's room in the modern shoeboxes.

And what do we gain ? Absolutely nothing at all until EVERY custoner on part of the network has been converted.

Conversely, any custoner is free to ignore the DNO provided earth and make their own arrangements - limited only by their access to sonewhere for a suitably earth electrode (system).

Lastly, who here has has the experience of connecting a 110V item to 240V ? Occasionally it's forgetting to check the position of the voltage selector switch. Once in my case it's been someone sending me the wrong (single voltage) part. But generally the results "aren't pretty".
So I would forsee a lot of blown up kit as people plug their 240V items into 400V supplies. Now they wouldn't ? I can assure you that a lot if oeople would - they have no idea what voltage is.
I recall at a previous place, the ladies in the retail shop asked the maintenance guy for some wire cutters. Why ? To cut off the plug and fit a new one on the christmas tree lights - it never occurred to then that the reason for an "odd" plug could be that the lights weren't 240V.

So, woukd 400V be a good idea ?
Possibly - but only if you don't start from here!
 
It doesn't have to be two legs of a 400/230V system. One night, the DNO could uplift your local 400/230V transformer and drop a 690/400 in its place, and presto! 400V Uo in your house.

Switchovers from one voltage or frequency to another and DC to AC have all been done before. When the National Grid drove a rollout of standardised voltage and frequency, electricity suppliers would take your appliances and either modify them for the new supply or replace it if not possible, just as gas appliances were converted from town gas to natural gas. In the museum we have appliances originally made for non-standard voltages that have been reworked and the new voltage engraved onto the plate. E.g. a Hoover vacuum cleaner made for 210V that had a replacement armature fitted and '240V' stamped over the 210. Until recently, a church with a 1920s organ blower wound for 200V was running it from 400 via a transformer supplied and fitted in the 1940s at the electricity supplier's cost. Sites with large inventories of DC plant used to install rectifiers to keep it all running when the mains were converted to AC.

The greater number of appliances in use today and the impracticality of converting most of them makes a repeat of that exercise near impossible, though.
 
It doesn't have to be two legs of a 400/230V system. One night, the DNO could uplift your local 400/230V transformer and drop a 690/400 in its place, and presto! 400V Uo in your house.

Switchovers from one voltage or frequency to another and DC to AC have all been done before. When the National Grid drove a rollout of standardised voltage and frequency, electricity suppliers would take your appliances and either modify them for the new supply or replace it if not possible, just as gas appliances were converted from town gas to natural gas. In the museum we have appliances originally made for non-standard voltages that have been reworked and the new voltage engraved onto the plate. E.g. a Hoover vacuum cleaner made for 210V that had a replacement armature fitted and '240V' stamped over the 210. Until recently, a church with a 1920s organ blower wound for 200V was running it from 400 via a transformer supplied and fitted in the 1940s at the electricity supplier's cost. Sites with large inventories of DC plant used to install rectifiers to keep it all running when the mains were converted to AC.

The greater number of appliances in use today and the impracticality of converting most of them makes a repeat of that exercise near impossible, though.

What was the highest single phase voltage ever used in the UK or anywhere in the world?
 
What safety comes from using a wall switch as a disconnecting means?

It is often, although not always that an isolator next to an appliance is not only a functional switch but also an isolator.
An oven or a shower would be a couple of things that spring to mind.
It would be unexpected for part of the appliance to remain live after you had switched it off
 
It doesn't have to be two legs of a 400/230V system. One night, the DNO could uplift your local 400/230V transformer and drop a 690/400 in its place, and presto! 400V Uo in your house.
But in the context that started this off, getting rid of combined neutral & earth, doing that wouldn't really help.
Switchovers from one voltage or frequency to another and DC to AC have all been done before.
Indeed, but back then there weren't huge numbers of appliances - and what there were would have been "properly built". As you point out ...
The greater number of appliances in use today and the impracticality of converting most of them makes a repeat of that exercise near impossible, though.
Indeed. Though I'd have gone further than "near impossible" ! I couldn't see it being done in any other way than lots of transformers. Just a very quick count around the house quickly heads up past 50, before I've included lights and fixed stuff like the boiler. Quite a lot of fixed stuff - PIR detectors, lights, heating controls, pumps, and the list goes on and on.

I think a lot of 25kVA transformers needed ![/QUOTE][/QUOTE]
 
It is often, although not always that an isolator next to an appliance is not only a functional switch but also an isolator.
An oven or a shower would be a couple of things that spring to mind.
It would be unexpected for part of the appliance to remain live after you had switched it off

Perhaps in the UK but not elsewhere. Keep in mind that close to 50% of the world's population deals with unpolarised schuko plugs on a daily basis.
 
Perhaps in the UK but not elsewhere. Keep in mind that close to 50% of the world's population deals with unpolarised schuko plugs on a daily basis.

That is different, a plug and socket IS A FORM OF DOUBLE POLE ISOLATION
 
I think people conventionally unplug an item if possible, or switch it off if not, before maintenance. The practical result is that with single-pole switching in the line conductor and a solidly grounded neutral, most permanently-installed lighting points are effectively safe to touch (although not isolated) with the switch off. With the increasing use of smart switches, points are more likely to be partially live during relamping and I am not sure that users are generally aware of this.

I was trying to isolate the question of the practicality of 400V appliances from Cookie's previous deliberations on the subject of distributing without a neutral. That might be what inspired this thread but whether a 400V SMPSU is electronically viable is quite a different topic from whether DP light switches are needed for safety. Taken together, then yes there is much to recommend star-grounding the supply to keep Uo at 230V and using two lines.

There is an important advantage of star-connecting single-phase loads to a three-phase system that must be considered. The 3-phase distribution cables, when subjected to diverse and typically balanced load comprising many small single-phase loads, carries little neutral current (except zero-sequence harmonics which are a nuisance whichever way things are wired.) Therefore one gets an implicit transformation, in which the load is taken at 230V but causes only the voltage drop and power loss associated with the same load at 400V. This is true also of the 120/240V split phase system in use in the USA, hence its popularity. Not distributing the neutral does not improve the voltage drop on the 3-phase segment but constrains the user to taking the power at 400V. The efficiency advantage occurs only within the single-phase segment of the wiring.
 
That is different, a plug and socket IS A FORM OF DOUBLE POLE ISOLATION


Right, when opening up the appliance or tool for service. However beyond that single pole switching is just as safe and gets the job done. You either double insulate or hook an earth wire to the metal. Polarity does not change that.
 
I think people conventionally unplug an item if possible, or switch it off if not, before maintenance. The practical result is that with single-pole switching in the line conductor and a solidly grounded neutral, most permanently-installed lighting points are effectively safe to touch (although not isolated) with the switch off. With the increasing use of smart switches, points are more likely to be partially live during relamping and I am not sure that users are generally aware of this.

I was trying to isolate the question of the practicality of 400V appliances from Cookie's previous deliberations on the subject of distributing without a neutral. That might be what inspired this thread but whether a 400V SMPSU is electronically viable is quite a different topic from whether DP light switches are needed for safety. Taken together, then yes there is much to recommend star-grounding the supply to keep Uo at 230V and using two lines.

There is an important advantage of star-connecting single-phase loads to a three-phase system that must be considered. The 3-phase distribution cables, when subjected to diverse and typically balanced load comprising many small single-phase loads, carries little neutral current (except zero-sequence harmonics which are a nuisance whichever way things are wired.) Therefore one gets an implicit transformation, in which the load is taken at 230V but causes only the voltage drop and power loss associated with the same load at 400V. This is true also of the 120/240V split phase system in use in the USA, hence its popularity. Not distributing the neutral does not improve the voltage drop on the 3-phase segment but constrains the user to taking the power at 400V. The efficiency advantage occurs only within the single-phase segment of the wiring.


Does the UK implement any forum of over-voltage protection should a neutral break?

Agree, but for the sake of the argument, there are advantages in not distributing a neutral. Many of which become greater with system size, number of sources and the presence of automatic transfer switches.

One must keep in mind there are countries like South America which derive 220 volts Line-Line when they could just as easily have gone 220/380Y.

Two options exist in theory:

1) Design all single phase equipment for 400 volt operation and use 230/400Y trafos.

2) Keep the present standard of 230 volts. Homes and small buildings supplied via 133/230Y trafos. Large buildings supplied via 277/480Y, 347/600Y or 400-415/690-720Y transformers. 690 volts is taken to directly to large motors and equipment while transformers seeded around the building take 690 volts down to 230Y for lighting and socket loads.

I'm left left wondering if the wire savings and efficiency of 690 volts along with lower dielectric requirements of 230 volt equipment outdoes the material cost of transformers, their associated losses and larger cable in smaller supplies.

Of course there is the 3rd option of 230/400Y with the neutral distributed taking into account the complexities of 4 pole isolation and protection against an open neutral.
 
Keep in mind that close to 50% of the world's population deals with unpolarised schuko plugs on a daily basis.
Do you have any feel for how many (what proportion) of appliances aimed at such markets use 2 pole switching internally ? I've only a limited sample, but a significant proportion of those I've ever had to look inside (especially things like drills and other hand-held tools) have had double pole switching. But as mentioned, it should be routine to pull the plug before opening anything up or poking things in - as a farmer I once worked for did, start clearing the air vents on an angle grinder with a metal pocket knife (he did quickly unplug it when I pointed out it was still plugged in).
Does the UK implement any forum of over-voltage protection should a neutral break?
Generally not - as attested to by news reports of household fires when some scrote nicks £20 of neutral link from the substation.
But it's not just the phase-neutral voltage that's an issue - and that could be dealt with by a voltage monitoring relay to disconnect the supply. There's an electrical safety issue in having the MET, and hence everything attached to it, at a potential that's very different to local earth. Not too bad inside where there's equipotential bonding, but bad news for someone leaning on their car and touching a metal bollard/lamp post/whatever nearby (and hence the extra requirements for charging points).
I was under the impression that the idea sparking off the original question was along the lines of "if people switched to 400V for single phase, we (or more correctly, the DNOs) could ditch the neutral and use the current combined N&E as an earth only for a TN-S supply".
One must keep in mind there are countries like South America which derive 220 volts Line-Line when they could just as easily have gone 220/380Y.
I worked very very briefly aboard a ship that used the same system - 3 wire 3 phase, 220V phase-phase and everything connected across 2 phases. Well to be more accurate, some things were like that, most of the ship was still 220V DC - they'd converted one generator to AC to allow all those AC appliances people like to have to work, while most large loads were still DC. I noted while doing a little electrical job in the engine room, that there was an air compressor driven by a motor with a higher power rating than my car engine !
Fortunately for them, all the circuit breakers (which must have been exceedingly modern for something built in the early 50s) were AC or DC so they only had to add a third wire to the main distribution boards and distribute the sub mains to the local boards across the 3 wires. So getting single phase AC to the hotel loads was fairly easy. The breakers were also 2 pole - I think all the system was floating and nominally +/-120V. I know the emergency lighting was as they had a pair of indicator lights by the battery tank to indicate if there was an earth fault - both lights dim and equal = nothing dragging one side of the DC to the hull.
And everything was originally labelled in Italian. And on push button starters, the red button was for start and the green button for stop - which seems much more sensible to me than pressing a green button to make something dangerous and a red button to make it safe o_O
 
Delta supplies are still popular afloat which adds complexity when speccing certain types of kit, e.g. entertainment lighting dimmers that take 3-phase input but control single-phase outgoing circuits. One of my colleagues recently succeeded in altering the specs for a number of forthcoming cruise ships, to include extra star-connected substation transformers for this application.
 
Delta supplies are still popular afloat which adds complexity when speccing certain types of kit, e.g. entertainment lighting dimmers that take 3-phase input but control single-phase outgoing circuits. One of my colleagues recently succeeded in altering the specs for a number of forthcoming cruise ships, to include extra star-connected substation transformers for this application.


Ungrounded Delta (IT earthing) does not offer any advantage (IMO) in typical applications- at best, at worst it leads to insulation break down. An intermediate or arcing fault can cause phase to earth voltages to rise 6-8x their normal values damaging the electrical system and the equipment its connected to. MOVs and electronics in particular have a hard time coping.


To remedy this you would go with either resonant or high resistance earthing, however unless you're dealing with critical process I don't see it being worth the complexity. Especially when ground fault indicators are typically ignored outside of Hospitals and industrial.

Of course you could add 30ma RCDs on circuits and a time delayed 500ma RCD on the main board nullifying the continuity of service. But one is left to argue, is it still worth the effort?
[automerge]1600550566[/automerge]
Do you have any feel for how many (what proportion) of appliances aimed at such markets use 2 pole switching internally ? I've only a limited sample, but a significant proportion of those I've ever had to look inside (especially things like drills and other hand-held tools) have had double pole switching. But as mentioned, it should be routine to pull the plug before opening anything up or poking things in - as a farmer I once worked for did, start clearing the air vents on an angle grinder with a metal pocket knife (he did quickly unplug it when I pointed out it was still plugged in).

Honestly, small 230 volt appliances seem to have single pole switching, while larger 230 volt appliances tend to have a double pole isolation main switch some place.

I still think schuko sockets have successfully shown that polarity and earth reference of the second line conductor should and does not dictate protection against electric shock.

Generally not - as attested to by news reports of household fires when some scrote nicks £20 of neutral link from the substation.

And right here is one of the biggest dangers of connecting loads phase to neutral.

In the US shared neutrals are common exiting the panel, if not right up to the light fitting or sockets. You have cases where a disconnected neutral results in hundreds of light fixtures being smoked in a warehouse or office building.


But it's not just the phase-neutral voltage that's an issue - and that could be dealt with by a voltage monitoring relay to disconnect the supply. There's an electrical safety issue in having the MET, and hence everything attached to it, at a potential that's very different to local earth. Not too bad inside where there's equipotential bonding, but bad news for someone leaning on their car and touching a metal bollard/lamp post/whatever nearby (and hence the extra requirements for charging points).

Yup, a very real danger with PENs.



I was under the impression that the idea sparking off the original question was along the lines of "if people switched to 400V for single phase, we (or more correctly, the DNOs) could ditch the neutral and use the current combined N&E as an earth only for a TN-S supply".

Correct. If all single phase equipment moved to 400 volts the DNO's PEN would become just a CPC.

I worked very very briefly aboard a ship that used the same system - 3 wire 3 phase, 220V phase-phase and everything connected across 2 phases. Well to be more accurate, some things were like that, most of the ship was still 220V DC - they'd converted one generator to AC to allow all those AC appliances people like to have to work, while most large loads were still DC. I noted while doing a little electrical job in the engine room, that there was an air compressor driven by a motor with a higher power rating than my car engine !
Fortunately for them, all the circuit breakers (which must have been exceedingly modern for something built in the early 50s) were AC or DC so they only had to add a third wire to the main distribution boards and distribute the sub mains to the local boards across the 3 wires. So getting single phase AC to the hotel loads was fairly easy. The breakers were also 2 pole - I think all the system was floating and nominally +/-120V. I know the emergency lighting was as they had a pair of indicator lights by the battery tank to indicate if there was an earth fault - both lights dim and equal = nothing dragging one side of the DC to the hull.
And everything was originally labelled in Italian. And on push button starters, the red button was for start and the green button for stop - which seems much more sensible to me than pressing a green button to make something dangerous and a red button to make it safe o_O

I know IEEE and IEC equipment seem to treat red and green differently. Protection relays for the IEEE market have green as open and red as closed, while those for IEC market have green as closed and red as open. Could be wrong but thats what I've personally seen.
 
Last edited:

Reply to Practicality of 400 volt equipment in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
A
Replies
29
Views
17K
amberleaf
A

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock