Hi we have been working on a student accommodation site . And have been installing PREFECT PRE9275 hob timer switch in a small copact kitchen. These have been getting installed only half an arms length away from the sink on the splash back. I am just wondering what is the minimum distance from a sink should the button switch be placed.
Thanks
P's would post a picture but don't know how :cheesy
 
Hi we have been working on a student accommodation site . And have been installing PREFECT PRE9275 hob timer switch in a small copact kitchen. These have been getting installed only half an arms length away from the sink on the splash back. I am just wondering what is the minimum distance from a sink should the button switch be placed.
Thanks
P's would post a picture but don't know how :cheesy


BS 7671 does not specify any minimum distance for socket-outlets to be from a sink. However, regulation 512.2.1 requires external influences to be considered when selecting equipment for a particular location. Accessories used in domestic installations are not designed to be splashed and therefore not suitable for installation close to a sink or draining board. For this reason, it is recommended that socket-outlets and other accessories should be located at least 300 mm, measured horizontally, from a sink or draining board, where they are less likely to get splashed.

The above is quoted by the ECA ^
 
Last edited:
Just reading ITE Electrician's Guide to The Build Regulations
Page 60

5.2.2 Location of accessories in kitchens
IV) Accessories should be installed a minimum of 300mm from the edge of kitchen sinks and draining oards to reduce the risk of being splashed.
 

Reply to Prefect pre2975 switch ? in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Evening Gents just after a bit of advice and what would you do differently. I have wired up 3 kw heaters in 4mm tuff cable (40 meter distance...
Replies
2
Views
260
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
445
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
840
Hi everyone, after temporary removing a Sonoff that I've installed years ago to do some painting, I'm unable to get everything back to work. I've...
Replies
4
Views
462
FYI --- This is a U.S. installation. I'm replacing a three way switch (the UK might more sensibly call it a two way switch??) with a Kasa Smart...
Replies
4
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock