- Reaction score
- 17,020
A parent at the school asked me why they might be going through a lot of appliances.
Washing machine less than 4 years.
kettle 3 years and LED lamps, less than 6 months.
There were other things, but can’t remember lifespan.
I popped in on passing one day and did a quick test on the kettle socket. (Didn’t go to the length of taking the db apart this time)
voltage was 248v, Zs at the socket was 0.91
TNC-S, not an overhead line, buried. But the houses are down a little valley, so I’m guessing they’re on the end of the supply cable.
They don’t know if any of the other houses have had the same issues.
20 year old installation, in a much older renovated cottage.
First thought was overvoltage, but 248 is high, but ok.
They haven’t noticed if any light brightness fluctuates, indicating fluctuating voltage, but I don’t think there is any tungsten lamps, all LED or cfl.
Anything else to look for if I go back for a proper visit?
Washing machine less than 4 years.
kettle 3 years and LED lamps, less than 6 months.
There were other things, but can’t remember lifespan.
I popped in on passing one day and did a quick test on the kettle socket. (Didn’t go to the length of taking the db apart this time)
voltage was 248v, Zs at the socket was 0.91
TNC-S, not an overhead line, buried. But the houses are down a little valley, so I’m guessing they’re on the end of the supply cable.
They don’t know if any of the other houses have had the same issues.
20 year old installation, in a much older renovated cottage.
First thought was overvoltage, but 248 is high, but ok.
They haven’t noticed if any light brightness fluctuates, indicating fluctuating voltage, but I don’t think there is any tungsten lamps, all LED or cfl.
Anything else to look for if I go back for a proper visit?