Currently reading:
problem with 60 amp fuse

Discuss problem with 60 amp fuse in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
I changed two fuse boards in a house that is converted into 6 flats, these 2 boards control the communal lighting, which work on PIR sensors, so are never left on for long, they also control the fire alarm, emergency lights and the immersion heaters, one on each board.
So in each fuse board we have a 32 amp ring, a 16 amp water heater circuit, a 16 amp radial socket circuit and 2 lighting(6 amp) circuits.
When i turn the power on everything is fine, but then when i leave the job, an hour or so later i have the landlord on the phone saying nothings working, when i go back the 60 amp fuse has blown, but it seems to take an hour or 2 to blow, can anyone shed any light on this for me as i've been back 3 times now and am going out of my mind.
thanx, james.​

 
measure the total current drawn on the 60A fuse. sounds like it's pulling about 90A. is there a cannabis farm in the attic?
 
^^^^^^^^^^^^^^As above^^^^^^^^^^^^^

Check for extension leads coming off sockets in communal areas (the landlord pays the bill for each flats electricity).

Worth staying around for an hour with your clip on Amp meter.
 
I had this problem before and it turned out that they supply cable from the fuse to the ccu had a snip where someone had cut of sheath and was arking cauding the fuse to blow you need to do an isulation resistance test on the cable or if its before the meter call dno
 
If that this case back out with the test gear and check double check everything from scrath !

I take it that its only the 60 A fuse blowing nothing else on the consumer side tripping on the new boards!
 
I would check the connections on the cutout/ryefield fuseholders that hold the 60a fuses that keep blowing.
If there is heat build up here due to loose terminations/fuse blades/contacts the heat could melt the fuse wire with only a few amps flowing.
By the time you return to site the fuseholder will have cooled down so you would never know.
 
A quick way to check for heat build up is the temperature sensing labels sold by RS. I’ve used them on fuses before. Will have a look for them later, busy cooking at the mo.

I bet it isn't Puy lentils in creme fraiche and white wine, salmon baked with lemon and garlic, new potatoes, 10 minute old asparagus and roast parsnips coated in butter???
 

Reply to problem with 60 amp fuse in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top