Hi Guys, im hoping someone can help me.
I have recently installed 3.2kw system for an offgrid job. The problem im getting is that im only ever seeing around 300 watts solar generation for the whole system.

We have used 10 x Canadian Solar 320 watt panels Voc for the panel is 44.9 and the ISC IS 9.08A also the short circuit current is 9.26
I have used Victron energy for my solar charger (150 volts/ 70 amp along with bi directional inverter.
I have had to wire them as 2 in series/ 2 in parallel for one mppt and 2 in series/ 3 in parallel for the other mppt to meet the solar chargers perimeters.
the actual voltage i am now getting is 87 volts at 8 amps per pair, but when i add them all together it stays the same (87 volts at 8 amps) the ampage does not add.

I have tested every panel individually and the voltage and ampage per panel is correct but them i carried out a short circuit current test and my highest reading was 1.34 amps out of the 10 panels.

I have triple checked the wiring and its not that, i have also had Victron take a look at the solar charger and even replaced it for a new one but also it was not that.

Its also not because the battery bank is fully charged either because its not.

Its not the weather either as it was a belter of a day but still the same.

Is it possible i have 10 x bad panels? Its never happened to me before but theres always a first.

I am scratching my head on this and have been back and forth for the last two weeks.

Any help on this and i would truly appreciate it.
 
you've probably wired several of the strings in reverse polarity.

The answer to these types of questions is usually reverse polarity, I'd triple check that before doing anything else.

I know it sounds basic, but it happens to the best of us, so it's always the first thing I triple check even when I wired it, or whoever else wired it swears blind that it was done right 90% of the time that's what it is.
 
you've probably wired several of the strings in reverse polarity.

The answer to these types of questions is usually reverse polarity, I'd triple check that before doing anything else.

I know it sounds basic, but it happens to the best of us, so it's always the first thing I triple check even when I wired it, or whoever else wired it swears blind that it was done right 90% of the time that's what it is.

Its not reverse polarity either, our solar charger wouldnt work if that was the case. Plus i checked that first.
 
Hi - just reading the thread - if it isn't wiring, then : do these panels come with individual test sheets? I'd get the light meter out to confirm what current you should get and contact the manufacturer for advice.
 
if it's dual MPPT inverter then it may well work on one side, and if you've got 2 strings the right way round, 1 the wrong way around then this would end up with it looking to the inverter as if it's got a single positive string.

I've heard too many electricians tell me it's definitely not reverse polarity I've checked, then be proved wrong - that's still what I'd put my money on.

Chances of it being the panels are miniscule.
 

Reply to Problems with Series/ Parallel strings not adding ampage. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
500
Im trying to make a Star Wars Prop for a course project where the dealine is comming up very fast in days and I need to do the report so really...
Replies
0
Views
388
New to the forum. Retired Navy Aviation Electrician with 25 additional years in automotive electrical systems - enough knowledge to be dangerous...
Replies
1
Views
922
hello guys this is my first post, i hope I am posting this one on the right section. aamseee I am looking for some advise. i have bought a...
Replies
1
Views
3K
I had solar installed professionally 3 years ago. The home is 10 years old and has 3 AFCI breakers for bedrooms. One AFCI circuit was hardly...
Replies
2
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock