Discuss Pros...cons...preferences.. in the UK Electrical Forum area at ElectriciansForums.net

Baddegg

-
Esteemed
Arms
Supporter
Patron
Reaction score
5,397
after my rather vague thread Friday about finding the 30 mtrs of 10mm 2 core swa In the back of me van.....after some views on earthing to the shed, 3 options as far as I’m aware are
1. Run a single 10mm from main met upto the shed and use that
2. Use the armour of the swa, adiabatic permitting..
3. Connect the swa to the main met at source end and TT the shed
Each option is appruthe same cost wise and it’s my own house so Labour is not a big issue, as per title just after others views and preferences....
 
Like you said,tt @ shed end then main bond any extraneous conductive part,water,steel.
Shed protected by Rcd,Swa protected by mcb & Main earthing system,job a good one.
 
after my rather vague thread Friday about finding the 30 mtrs of 10mm 2 core swa In the back of me van.....after some views on earthing to the shed, 3 options as far as I’m aware are
1. Run a single 10mm from main met upto the shed and use that
2. Use the armour of the swa, adiabatic permitting..
3. Connect the swa to the main met at source end and TT the shed
Each option is appruthe same cost wise and it’s my own house so Labour is not a big issue, as per title just after others views and preferences....
appruthe??? WTF does that mean?????
 

Reply to Pros...cons...preferences.. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m a trainee electrician and would really appreciate the benefit of someone’s skill and experience on the following: Our house is a TN-C-S (100A...
Replies
70
Views
6K
Evening all. I have a question as I can’t get my head around something with solar PV I’m going to be working on a new build in a couple of...
Replies
9
Views
3K
I'm planning to build a shed in the far RH corner of the rear garden. It will have a reinforced concrete base, wood structure, flat roof and be...
Replies
0
Views
2K
Short Version Is it permissible to have 2 feeds to 2 separate consumer units in a detached garage? Is it permissible to run SWA underground...
Replies
15
Views
3K
I am considering the options which may apply to the earthing arrangement for a supply to a wooden shed. The property has a TN-C-S supply from...
Replies
8
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock