L

LearnerDave

Hi Guys,

We measured PSCC on a three phase dist board in a commercial establishment. This board is fed from a main switch board with a main 400Amp switchfuse with BS88-2 fuses rated at 88kA. Feeding a second 160Amp switchfuse with BS88-2 fuses protecting the cabling to the board we were looking at.

The board has Dorman Smith series 15 MCBs rated at a PSCC of M4.5 which I believe = 4.5kA. We measured the highest PSCC/PEFC as 2.9kA. I believe the rule of thumb is to double it, which = 5.8kA. This meant the value is larger than the rated kA of the MCB .

In GN3 I’ve read that - Reg. 434.5.1 states that the breaking capacity rating of each protective device shall be not less than the prospective fault current at its point of installation. From this I would say that the MCB would have to be higher rated than the measured kA and therefore in this case need to be changed. One of the other chaps said because the board was supplied by a BS88-2 88kA fuse, there wasn’t an issue as this has the capability to blow its fuse safely. I can’t find anything in the Reg’s to back this up.

Is it acceptable to rely on the up stream BS88-2 fuse? If not, how serious/necessary is it to up-rate the MCB?
Out of interest, what PIR code would you give it, if any?

Thanks a lot Dave
 
Last edited by a moderator:
if you are measuring the pscc before the dorman MCBs. i.e on the incoming side of the board , it is the fuses feeding this board that have to withstand the pscc.
 
Hi Telectrix, It was measured at the incomer of the Dorman Smith board.

If It was measured on the load terminal of the MCB's and got a similar reading, am I correct in thinking that a dead short in the cable just after the MCB could theoretically allow the measured PFC to flow through the MCB and if larger than the MCB rating could destroy it, and may not work/open at all?
 
theoretically, yes. in practice unlikely. better minds than mine may disagree.
 

Reply to Prospective Fault Current in the Canada area at ElectriciansForums.net

Similar Threads

Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
During a recent inspection on a 3 phase board I have some MCBs rated at 6KA And some rated at 10 KA . The ZE is about 0.04 to 0.05 depending on...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock