It's under schedule of items tested.
If you mean "presence of protective conductors" if you look closer it also ask about presence of Earthing and bonding conductors protective conductors mean cpc.
 
Can you state what it actually says along with any Reg Nos if applicable as I have no idea what the Easycert formats contain.
 
See line 13.3 on picture.

The distribution board that this cert refers to does not have any main protective conductors to supplies. So I was asking in your opinion this means cpc for final circuits or just main protective conductors.

15072976319261421851024.jpg
 
Protective conductors would cover circuit protective conductors (cpcs) and the earthing conductor at source of supply. As there is no mention of main protective bonding conductors it probably includes these as they are also protective conductors.
 
Protective conductors would cover circuit protective conductors (cpcs) and the earthing conductor at source of supply. As there is no mention of main protective bonding conductors it probably includes these as they are also protective conductors.
I tend to agree looking at the form the OP has provided, the one I looked at mentioned all 3 for the presence of:
Protective
Bonding
Earthing
Makes you wonder how some folk can get confused
 
The Easy Cert form your using appears to refer to both cpc's and main protective bonding conductors in this one tick box. The one I use has separate tick boxes. Whatever you would of carried out some tests to verify, and for cpc's have a specific reading.
 
The Easy Cert form your using appears to refer to both cpc's and main protective bonding conductors in this one tick box. The one I use has separate tick boxes. Whatever you would of carried out some tests to verify, and for cpc's have a specific reading
you are correct there.
on that test sheet 13.2 on BYB 3.0to 3.8 /earthing and bonding arrangement's 411.3
but the person who made that test sheet should have made it more plain with out
copying the regs for copy righting.
 

Reply to Protective conductors on an EIC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
692
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Is it acceptable to lim on eic for supply characteristics? I had a job in a hospital today and I couldnt gain access to the Switch room and the...
Replies
9
Views
1K
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
758
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
633

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock