Discuss Protocol on RCD trip problems after new CU install in the Australia area at ElectriciansForums.net

S

SW1970

Hi folks, did PIR. No issues with cabling etc but outcome was replacement CU due to no RCD. Installed replacement CU but due to some faulty components from the supplier and faff over getting replacements didn't energise until 5pm. Going through a few tests and discovered RCD tripping on a kitchen ring (including freezer). Problem didn't appear until circuit was put under load with an electric kettle. Took ages fault finding and hadn't found it at 10pm. Client (senior citizen) was getting edgy and wanted to go to bed. CU is high integrity, had to leave the installation with kitchen ring on non-RCD slot, and cover off CU. CU is in downstairs loo. Explained situation to client, shut door to downstairs loo and told client not to open it at all and call me if any electrical problems arise, would go back early in am to continue fault finding. Went back in the am and then found fault within half an hour (micro cut in N cable touching metal back box behind socket).

Questions are:

1. Did I do the right thing leaving installation as I did overnight? Wasn't comfortable at all but client understood situation and agreed not to go into downstairs loo. One of those tricky situations where didn't really have a choice.

2. Is it worth having a temporary board set up with an RCD and prior to taking off old CU connecting each circuit up one at a time on temporary board to see if RCD holds? Haven't done this so far but after this job feel it could save a right load of hassle at least form the point of understanding where problems might crop up. Does anyone do this?

Many thanks, SW
 
1. NEVER leave a CU with the cover off, especially if it is energised. You will fail your assessment over this.

2. All your IR tests that you did in your pre install would have picked this up which, if they were not clear, meant there was a problem.
 
First question from me, I am just curious

Why leave the cover off the consumer unit and thereby ban the old gent from the Loo ?

He had no Rcd before the consumer unit was changed,I cant see that would have been too big an issue not having one for another night

Why a temporary board ? you have a board that can do exactly the same as a temporary board

Was there no indication of neutral-earth faults during testing ?the applied load taking out the Rcd indicates it would be evident on test
 
just wondering why CU cover had to be left off. agrre with Jason here. but have had good IR readings occasionally but RCD still tripping due to intermittent leakage fault due to nicked cables.
 
Thanks Jason - I get that. IR test were fine. Problem only appeared with circuit under higher load.

Des - 2 other loo's so old gent ok. No N-E faults during testing. Did it all again when fault appeared and still nothing came up. Temp connection to temp board on floor idea - just thinking about how to avoid this again in the future.
 
He found the fault which was a trapped N in a backbox.

A bit like the one i had a few weeks back :D

cable.jpg
 
No nicked neutral, did IR test between the neutrals and high IR so ok. Micro slice in cable was about a quarter of the size in Jasons photo & wasn't done by screw.
 
He found the fault which was a trapped N in a backbox.

A bit like the one i had a few weeks back :D

cable.jpg


Folks,dont think for a moment that was an inspection job
That was on Jasons latest new install
He had a few coils of red and black hanging around
icon6.png



The neutral fault was his punishment for being shoddy
icon7.png



Only joking, honest,its not worth a ban,really it isn't
icon11.png
icon7.png
 

Reply to Protocol on RCD trip problems after new CU install in the Australia area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
806
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
922

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock