dlt27

-
Reaction score
26
Hi, any help would be greatly appreciated. I’ve been asked to wire up a second hand 3 phase pto generator to an existing generator switch (see pictures). What I would like some advice on is; 1. Should the generator have its own earth electrode or can it be earthed to existing electrode. 2 . Should the main neutral be kept separate from the generator neutral at generator switch ( I’m presuming it should). 3. I am worried the pto has no voltage regulator so worried the dairies electronics might get damaged if RPM is too high. Not sure if to take the job on, but would still like to improve my knowledge on this type of generator even if I don’t!! Thanks again for any help.
 

Attachments

  • E752B796-C9F1-4821-A2D5-0AF51F260DB7.jpeg
    420.3 KB · Views: 26
  • 1FC42B4B-2854-4C95-9D35-F8016792E10B.jpeg
    417.7 KB · Views: 25
  • 02320B97-E2D1-454B-964B-400B4DF51B94.jpeg
    372.7 KB · Views: 24
  • 9D8D297F-1E55-438D-96C5-97FF3CD65B49.jpeg
    599.5 KB · Views: 21
  • 3C26BF0E-A22B-4C7B-9312-8AE6E1CE5265.jpeg
    429 KB · Views: 25
Wired up a few of these, although mostly single phase.
You need to provide earthing arrangements that would be adequate with the suppliers earth connected., but permanently connected in parallel.
All live conductors, which includes the neutral must be switched.
There should be a frequency indicator, rather than a voltage indicator connected to the generator. This either has a traffic light (red, amber, green) display or a single flashing amber light display, where the PTO speed is adjusted so that the light flashes very slowly.
These generators were usually supplied with change over switches, sized to the output of the generator. In a lot of cases these were not suitable, because the switch needs to be rated to match the maximum possible load, which was often much greater than the generator output.
An isolator should be fitted to the incoming supply before the changeover switch, which should be turned off before the C/O switch is operated. Looks like you already have this in place.
It can be handy to have an indicator lamp to show when mains power is restored.
Educate the farmer on how much tractor power these things can take. They think they take next to nothing, since the shaft can easily be turned before load is applied. Make sure they know better than to switch the C/O with the genny up to speed and a heavy load connected. I once saw a farmer do this, and the tractor was nearly flipped onto its side.
 

Reply to PTO generator connection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
537
hello guys, hope you’re all well. We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric...
Replies
5
Views
1K
I want to use a manual change over switch to safely connect a 21kVA single phase tractor PTO powered generator to my mains supply in case of...
Replies
20
Views
3K
I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
291
Hi Sorry to bring this one up again but have read numerous posts and answers and not got an answer specific to my situation. I have a Loncin...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock